    Heat Pump Cascades and buffers



    We are designing a system to include 2 heat pumps both feeding into 1 buffer. 1 will act as the lead unit, having hot water responsibility along with space heating. They will both tee together on the flow and return to the buffer. The second unit will only have an influence on space heating.

    We usually assume 30 litres per kw from advice on here earlier, but do we size on the combined output of the 2 units or just on the lead unit given that this will have responsibility for initially heating the buffer?

    The units are both 16kw air source.

    Any advice would be greatly appreciated.

    Cheers

    Jon



  2. #2
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Heat Pump Cascades and buffers

    You'll be fine on sizing for one unit John, as if the second unit is required to heat it means there is already a large draw off the buffer. The buffer will allow enough flow (once its a direct cylinder) for both units to operate at once and defrost correctly

  3. #3
    Join Date
    Jan 2011
    Location
    UK
    Age
    54
    Posts
    78
    Rep Power
    14

    Re: Heat Pump Cascades and buffers

    Thanks BF we thought this was the case but just wanted to be sure before we specced.

    Cheers

    Jon