Thread: Daikin muliti unit
08-04-2011, 06:25 PM #1
Daikin muliti unit
hi I have a daikin multi unit on one Ftxs 35 and two Ftxs 25 these units are on r22 one of the Ftxs 25 is not cooling or heating the other two are fine the gas pressure is fine can any one help
Jason
08-04-2011, 11:14 PM #2
Re: Daikin muliti unit
Are there any fault codes showing or in the unit history?
If the unit is not running how do you know that the gas pressure is fine?Brian - Newton Abbot, Devon, UK
09-04-2011, 06:07 PM #3
Is the green operation lamps flashing on the one that does not cool?
10-04-2011, 04:01 AM #4
On the two other units they are cooling perfect tried the fault codes nothing has come up and the outdoor runs
10-04-2011, 04:02 AM #5
No green light flashing on the one that does not work
10-04-2011, 08:12 PM #6
As the outdoor unit can only heat or cool, but not at the same time, the indoor units must also be in the same mode to operate. If 1 of the indoor units is in a different mode, the green operation lamp will flash to tell you it is in standby mode when you switch it on.
If this is not happening, then you need to look at the pcb to determine if it has power and the HP1 LED is flashing
13-04-2011, 08:20 PM #7
All the modes are on cooling and the hp1 is flashing who nos