    high coldroom temperature



    Hi Guys,

    I have a 2 forced fan evaporator.Client stopped equipment for a month and when started up did not go down to -18 degrees celcius but remained to -2 degrees.I asked to turn off,and started it myself again.R404A.I read the following.

    Ambient temperature 22.3 celcius.
    Suction pressure 22 psig/ 1.5B
    Discharge pressure 175psig/11.9B
    Liquid line pressure 175 psig/11.9B

    Thermometre readings.

    After half hour running with sight glass clear and same pressures.
    Suction temp 3.8 celc
    Discharge temp 65.6 celc
    Liquid line temp 38.5 celc.

    Air off condenser fans 26.4 celc,entering 22.3 celc.
    Air off evaporator fan/s -1 deg celc.
    Room temperature -1 celc.
    Inspection of txv having apartial frosting of evaporator.


    What can be the reason of not getting the temperature down.I asked client to await till tomoroow morning and recheck temperature.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: high coldroom temperature

    How long does the room normally take to pull down to temperature?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: high coldroom temperature

    Replace the refrigerant with a virgin one.
    I have seen this hapening a few times. The best is to use 507.

  4. #4
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: high coldroom temperature

    This is the first time being on this plant,but left it working for 2 hours and did not drop below -2 celc from +8 celc.

  5. #5
    Join Date
    Dec 2009
    Location
    Ireland
    Age
    36
    Posts
    14
    Rep Power
    0

    Re: high coldroom temperature

    if u have a back pressure of 1.5 Bar thats very low pressure whats is your coil temp?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: high coldroom temperature

    Suction pressure of 1,5 bar is -25°C
    Suction temperature is 3,8°C! Where is it measured?
    At -2°C coldroom temperature evaporation temperature should be -12°C to -17°C.

    Liqud line pressure 11,9 is 26°C condensation. Entering air is 22,3°C. Condensation should be at least 32-35°C.
    Liquid line temperature is 38,5°C. That mean no subcooling.
    You are probably short of gas!

  7. #7
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: high coldroom temperature

    Quote Originally Posted by nike123 View Post
    Suction pressure of 1,5 bar is -25°C
    Suction temperature is 3,8°C! Where is it measured?
    At -2°C coldroom temperature evaporation temperature should be -12°C to -17°C.

    Liqud line pressure 11,9 is 26°C condensation. Entering air is 22,3°C. Condensation should be at least 32-35°C.
    Liquid line temperature is 38,5°C. That mean no subcooling.
    You are probably short of gas!
    If you are short of gas so probably the compressor or the group of compressors is working at low partial capacity. Kerrcell do you confirm that?
    OR only remains the two low pressure components of blend refrigerant (the R134a and the R143a) the high pressure component (R125) was gone.
    To make progress is never good enough, I want to do better and better and better

  8. #8
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: high coldroom temperature

    Hi guys,

    I read suction temperature at close to compressor,not in the evaporator.Did not take the reading inside the evaporator! I did suspect that charge is low but obviously one cannot just start filling up with gas and then will find that has to take agaain part of it away if not in full ! This morning called the client and he said that during the night temperature dropped to -5,not more.The fact that the evaporator is partially frosted,drives me to lach of charge.Will recheck with client later today,if temperature,still the same,will collect what is in system.Then evacuate and refill by new gas R404A.

  9. #9
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: high coldroom temperature

    What's the % compressor capacity? Also if there is some kind of obstruction on the suction pipe (suction filter dirty or a valve partially close) then that will cause the present effect because the evaporating temperature would be much higher and consequently less capacity.
    To make progress is never good enough, I want to do better and better and better

  10. #10
    Join Date
    Dec 2008
    Location
    Bucharest
    Age
    44
    Posts
    50
    Rep Power
    16

    Re: high coldroom temperature

    The cold room was empty when is start to work ?
    Best regards,
    HVAC - service technician

  11. #11
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: high coldroom temperature

    Yes the cold room was empty.I think it takes longer to drop down the temperature.Could not get in touch with client to confirm temperature but will update tomorrow.Thanks for now

  12. #12
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: high coldroom temperature

    Guys last night we had a total power cut whole country,will update tomorrow with temperature.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: high coldroom temperature

    Quote Originally Posted by nike123 View Post
    At -2°C coldroom temperature evaporation temperature should be -12°C to -17°C.
    I made mistake here, it should be -7°C to -12°C.

  14. #14
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: high coldroom temperature

    Quote Originally Posted by nike123 View Post
    I made mistake here, it should be -7°C to -12°C.

    ...But if with a so big DT1 the suction pressure is so lower with a high superheat that really could mean short of refrigerant or other causes already pointed.
    To make progress is never good enough, I want to do better and better and better

  15. #15
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: high coldroom temperature

    Morning Guys,

    It seems all getting to the better,reading a temperature of -9 celcius.Cannot figure out what happened.I called on phone,did not visit back.I will leave it as it is for the moment and recheck.
    Thanks for now.

  16. #16
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: high coldroom temperature

    If the cold store is empty, no in/out of product it is strange that the cold store takes to long down the temperature.

    How much m3 have the cold store? What kind of insulation is applied on the cold store?
    To make progress is never good enough, I want to do better and better and better

  17. #17
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: high coldroom temperature

    The cold room is small.Measuring 8 by 8 by 7 feet high.Now temperature is -14 degrees celcius.It is old and so the insulation been never changed since.Coldroom been running around 9 years.But the compressor was changed around 4 years ago.The condenser coil has an area that is very corroded,as they washing it with tap water frequently to cool down in summer peaks !! Best thing to leave it running and see to what temperature it can drop best ! I thing there was a messup in this coldroom.

  18. #18
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: high coldroom temperature

    hmm...when the cold room be working normally with inlets and outlets of product I doubt it will do a good job. Let see what it happen and then keep us informed.
    To make progress is never good enough, I want to do better and better and better

  19. #19
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: high coldroom temperature

    Very important parameter you didn't gave us: SH of evaporator
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  20. #20
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: high coldroom temperature

    Hi peter1,

    Yes unfortunately did not take it.To tell you the truth,client did not bother as temperature got down more ,now reading -14 degrees celcius.He also started filling it up.He installed also plastic curtain as there not.He prefered to leave it as it is,so happy him,happy me.By the way he did not ask for bill !!!!!!!! So better keep expenses to the minimum.

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: high coldroom temperature

    Why would he ask for a bill? It is your work and money and you need to give him a bill, if you wish to collect money for your service.

  22. #22
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: high coldroom temperature

    Yep,but it looks as if I did nothing to solve his problem ! Temperature gradually went down.So best thing is to add a little extra next time I visit on something.That's better.

  23. #23
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: high coldroom temperature

    yes, I agree we must know I to deal with the Clients...specially the one that are very "complicated".
    To make progress is never good enough, I want to do better and better and better

  24. #24
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: high coldroom temperature

    i would just for argument sakes recover refrigerant replace liquid line drier, obviously pull full vac and recharge with virgin refrigerant.
    at least this will rule out if you have lost part of refrigerant blend.

    then start again if problem does persist at least you have ruled out a major possible fault.
    your only as good as your last job

  25. #25
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: high coldroom temperature

    All clients are complicated .................