    "lack of refrigerant alarm"



    Good day to all,

    Summer is approaching very fast in our region; in which we are staring to encounter "lack of refrigerant alarm" in our chiller packs system. We check all the possible causes like leaks, suction and discharge pressure as well as the ampere reading and all other areas in which the fault was related, but everything was normal. Can you help me to figured out what are the other possible causes of this alarm.

    Thanks and God bless,

    szanch18



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: "lack of refrigerant alarm"

    Is the alarm level set correctly?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: "lack of refrigerant alarm"

    If you measured all, you should submit data here:
    Here is a list of the temps/pressures needed to troubleshoot a system:

    Evap air/water in temp
    Evap air/water out temp
    Low side pressure or saturation temp
    Suction line temp at evap outlet
    Suction line temp at compressor inlet

    Cond air/water in temp
    Cond air/water out temp
    High side pressure or saturation temp
    Liquid line temp at receiver or condenser outlet
    Liquid line temp at TXV inlet
    The more information provided the more accurate the diagnosis.