    electronic expansion valve issue



    Hi sir,
    Could you tell me your idea of how to match EXV with variable frequency compressor? which paremeter is good as control point?

    rgds
    LC



  2. #2
    Join Date
    Aug 2005
    Location
    South Africa
    Age
    48
    Posts
    13
    Rep Power
    0

    Re: electronic expansion valve issue

    Hi LC

    I'm not sure if i'm thinking along the same lines as what you are but you should size your valve at full load. Most EXV's are able to operate down to 10% of it's rated capacity quite accurately. As the capacity of the compressor drops your valve should shut down accordingly

  3. #3
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: electronic expansion valve issue

    There are more approaches to control electronic expansion valve, as far as I know:
    1. Two temparature sensors before and after the evaporator. Then it controls the superheat just like the normal thermostatic. It works quite fine also with variable speed compressors. This method uses also the ALCO EXV Valve with its driver.
    look at this flyer
    2. Indirect superheat control according to discharge temperature after the compressor, but this method require special treating at frequency change as the response is slower. I do not recommend this. I think this is used only for budget reasons as there is less inputs. (Daikin Inverter Splits uses this method)

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: electronic expansion valve issue

    (Daikin Inverter Splits uses this method)
    From all the information I have, based on the Daikin training courses, this is an incorrect statement.

    I would be interested to see the information you have.

  5. #5
    Join Date
    Sep 2005
    Location
    Hampshire
    Age
    43
    Posts
    16
    Rep Power
    0

    Re: electronic expansion valve issue

    As with any expansion device it is selected based on the tonnage/kw capacity and specific to what ever refrigerant the unit is operating on but you need correct controls in place if you where to replace a txv for a exv

  6. #6
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: electronic expansion valve issue

    Hi dear all
    Thanks for your information.

    Frank,
    How about Daikin split unit? Do you have some information?

    rgds
    LC

  7. #7
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: electronic expansion valve issue

    to frank:
    for example SiE04-306 Inverter pair wall mounted type B-series
    Attached Images Attached Images

  8. #8
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: electronic expansion valve issue

    OK, maybe there could be some misunderstandig me, because I wrote, that only discharge temperature is used as controlled value.
    If I wanted to be exact, I should write, that there are thermistors on the evaporator and condenser, and from these temperatures is the target discharge temperature calculated.

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: electronic expansion valve issue

    Martind

    I know understand what you were trying to say

  10. #10
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: electronic expansion valve issue

    Hi Martind,
    My understanding is the valve opening decided by compressor frequency and the evaporator superheat. I'm not sure if there is a control table inserted in controller. What about daikin's controller? thx

    rgds
    Lichuan

  11. #11
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: electronic expansion valve issue

    We are leading this thread wrong way. It does not matter, how the proprietary control works, I used it only as an example. You cannot buy the valve and driver working this way (at least in our territory).
    I did not program the controller, but there should be something I think there would be some given shift (so not the absolute, but the relative value of the opening)
    Let it be, if you want to use electronic expansion valve, use the standard control, as I mentioned e.g. Alco or Danfoss.

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: electronic expansion valve issue

    Quote Originally Posted by lc_shi
    My understanding is the valve opening decided by compressor frequency and the evaporator superheat. I'm not sure if there is a control table inserted in controller. What about daikin's controller?
    I should say Lichuan, whatever the frequency of the compressor may be, the EEV has to be regulated in such a way that the superheat remains the same.
    Last edited by Peter_1; 27-09-2005 at 06:20 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: electronic expansion valve issue

    Hi Peter,
    Yeah. Keep the superheat same at any frequency. It's the advantage of EEV ,for TEV ,I think it couldn't control the same superheat.

    thanks for Martind's offering good opinion

    rgd
    LC-

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: electronic expansion valve issue

    I was told by someone of Mitsibushi Belgium that they measure twice temperatures to control the EEV in the VRF but one temperature is converted via the software in the machine to a pressure.

    They have installed somewhere - haven't seen it only but on the drawings - a small capillary which injects the liquid in a small tube. In that tube is one of the 2 previous mentioned themistor installed.

    Due to the small isolated tube and the small amount of liquid, there's almost no heat exchange, so they're measuring almost precisely the evaporating temperature which they then convert to evaporating presure.

    They avoid with this an expensive pressures sensor.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Nov 2007
    Location
    Jakarta
    Age
    75
    Posts
    11
    Rep Power
    0

    Re: electronic expansion valve issue

    Hi,
    Any body can help me for Electronic Expansion valve of Streamline Muller Industries model 2GB403144,465-PSIG-32-BAR used on Carrier water chiller of 370 KW cooling capacity.

    We got problem with this valve, the valve did not open properly on maximum compressor load.
    The system always shut-off caused by low suction pressure.

    Please help me. Thanks for your attention.
    Last edited by maguro4448; 13-03-2008 at 02:45 AM. Reason: can not find the problems

  16. #16
    Join Date
    Mar 2008
    Location
    Chicago
    Age
    60
    Posts
    7
    Rep Power
    0

    Re: electronic expansion valve issue

    I have worked on a few carrier flowtronics with the EXV .you can check the driver board of the exv . I think the valves have like 15000 steps and work on a pulse signal generated from the board . Most of the time i change out the valve and solves the problem . they change the style of the valve a few years back .

  17. #17
    non-pro's Avatar
    non-pro Guest

    Re: electronic expansion valve issue

    I know that I'm "dumbing down" the conversation with my question but I'm just a flakey salesman who is making an attempt to learn. Here's my question: Doesn't an EEV automatically set the superheat when used in conjunction with thermistors and a microprosser control board? Do the thermistors on the coil merely create algorithms to develop demand defrost cycles? I apologize for asking such a pedestrian question and I appreciate any insight given.

  18. #18
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: electronic expansion valve issue

    Firstly you need to know what a superheated vapour, subcooled liquid and a saturated vapour is, perhaps google the terms to find out the meanings.

    In this instance we want to control how superheated the vapour is leaving the evaporator, to do that you need to measure the difference between the temp the refrigerant is boiling off at inside the evaporator and the temperature of the vapour leaving the coil after it has turned into a vapour. For an EEV controller to measure the temp of the refrigerant boiling in the evaporator it is best to use a pressure transducer to read the pressure of the refrigerant - refrigerants have a direct pressure/temp relationship therefore the pressure can easily be turned into a temperature (saturated suction temperature), a crude way to do it is to measure the temp of the pipe where refrigerant enters the evap but this has quite a few factors that affect the pipe temp and cannot always be used accurately. By measuring the pipe temperature of the vapour leaving the coil we can determine the superheat (leaving temp - saturated suction temp = superheat).

    Too much superheat and we decrease the efficiency of the coil, too little superheat and we risk liquid refrigerant spilling out of the evaporator and back to the compressor which can damage the compressor. An EEV is merely an expansion device for metering refrigerant, the amount it meters in is dependant on the programming of the microprocessor. The microprocessor uses the thermistors (and hopefully a pressure transducer) to measure the condition of the evaporator and assess the superheat, from this information it uses some user programmable parameters along with inbuilt algorithms to adjust how much refrigerant is fed to the evaporator.

    Hope this helps.
    Last edited by 750 Valve; 12-06-2009 at 11:33 AM.
    ...and she said "give it to me you big fridgie"

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM
  3. Replies: 2
    Last Post: 07-09-2005, 03:07 PM
  4. pressure drop between expansion valve and distributor
    By aygul in forum Technical Speculations
    Replies: 10
    Last Post: 22-01-2004, 09:47 AM
  5. Oversizing EXV electronic expansion valve
    By aygul in forum Technical Discussions
    Replies: 5
    Last Post: 20-11-2003, 01:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •