Results 1 to 9 of 9
    Jan 2011
    Cheshire
    41
    26
    Which Ester Oil?
    I have cellar Cooling System running on R407c. The Compressor (Copeland Scroll) is low on oil. I know I need an Ester oil But which one? I took note where the compressor says POE but the only other details were the amounts it needs in 0z and L. Also where should the oil level sit on the sight glass? I want to avoid taking the old oil out and re-charging if I can.
    Thanks in advance guy's!!
    Somerset
    69
    4,697
    Re: Which Ester Oil?
    Hi BigGreenfridge.
    The attached may help clarify a few things.
    Somerset
    69
    4,697
    Also refer to this data.
    3,856
    Emkarate 32 MAF oil, available in 1L tins from climate. I'd aim for an oil level between 1/2 and 3/4 full with the comp off. Sometimes with those scrolls they seem to spin the oil round in the sump like stiring a cup of tea so it's difficult to get a good idea when they are running. Also need to run it long enough to be sure all the round the system has returned, especially if it has lost refrigerant at the same time as the oil that is missing. Also bear in mind too frequent cycling will pump the oil out quicker than it returns.
    Jan 2011
    Cheshire
    41
    26
    Thanks Guys, Some really usefull info there!
    May 2006
    India
    74
    399
    You can use FUCHS , DEA TRITON SE 55 ester ol for R-407C but check with Copeland ..............
    Feb 2010
    242
    All the other advice is good but you need to find where the oil went before adding
    new. I know you would do that anyway, so I'm teaching you how to suck eggs
    but don't add oil if the oil has not leaked out. Find out where the oil is.
    coolrunings
    Spencer ma.
    108
    Do not add oil till you know where it went as Coolrunings said.
    How can you tell its low on oil?
    Look @ the hole system not just one part.
    Jan 2011
    Cheshire
    41
    26
    I'd previously been and repaired a leak. There's oil all over the consensing unit so I'm pretty sure where most of the oil went
    All input is good input guys, sucking eggs or not!! Cheers
