    Ammonia alarm detection.



    I currently have a client that insists via there company policy of detection levels for alarming and evacuation, which I regard as totally rediculous.
    Example:- Low level alarm 25ppm, controlled evacuation, High level 35ppm total evacuation and Fire Service attend on site, weighted average zero.
    The total plant is 20 odd years old, glands leak, the plant is not smelly.
    My reaction is, bad breath and body odour would set alarm off, they have computer monitoring and the levels bounce around constantly.
    This is a GF group company, which is relative to the Australasia region , OZ and NZ.
    Typical case of OH& S gone mad.
    Check 25ppm/ 1000000.00ppm average a bees whisker. The draeger sensors are a there absolute minimum sensitivity and reaction reliability range. The staff spend a lot of time at assembly /evac., areas.
    Comments from Australasia and others please



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Ammonia alarm detection.

    Personnel protection 25/35ppm. in work areas or areas Yes.

    But not in a plant room.I am now seeing similar in the UK.
    What are the Industry guidelines for your part of the world?
    Grizzly

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Ammonia alarm detection.

    Hi Grizzly.
    thanks for comment, I think I have convinced client to partition the alarm monitoring system to 1/ process area at 25/35ppm, and 2/ the unmanned plant room, at a set of higher levels. I thinking of low level at 100ppm and high at 350ppm. All with a time waited average. The plant room has all the remote trigger and isolation of power etc., and ep extraction fans and lights, wash showers etc., to comply with local codes.

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ammonia alarm detection.

    Hi, Magoo

    Quote Originally Posted by Magoo View Post
    I currently have a client that insists via there company policy of detection levels for alarming and evacuation, which I regard as totally rediculous.
    Example:- Low level alarm 25ppm, controlled evacuation, High level 35ppm total evacuation and Fire Service attend on site, weighted average zero.
    The total plant is 20 odd years old, glands leak, the plant is not smelly.
    My reaction is, bad breath and body odour would set alarm off, they have computer monitoring and the levels bounce around constantly.
    This is a GF group company, which is relative to the Australasia region , OZ and NZ.
    Typical case of OH& S gone mad.
    Check 25ppm/ 1000000.00ppm average a bees whisker. The draeger sensors are a there absolute minimum sensitivity and reaction reliability range. The staff spend a lot of time at assembly /evac., areas.
    Comments from Australasia and others please
    Sorry for you ... please chek my sig.... in this case the second row ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.