    floating head pressures-nh3



    We recently installed the hench system to control electrical costs. The problem is getting the head pressure to stay stable. We reun 3 boosters @ 2 psig suction 32 discharge 4 high stage 32 suction 140 discharge . problem is head pressures are floating from 146 down to 100 psig creating an unstable condition and cooler than recomended oil temps on the high stages . Anyone have a suggestion on remedy for this problem? Thanks Mike



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: floating head pressures-nh3

    unilevermike,
    What is your oil temps getting down too?

    Also what type or screws are you running?

    In some cases a AMOT type valve is installed to bypass oil cooler
    Another way is a seperate cooling tower for oil coolers is used, cycing fan or VFD
    to control water temp.

  3. #3
    Join Date
    May 2010
    Location
    baltimore
    Age
    62
    Posts
    6
    Rep Power
    0

    Re: floating head pressures-nh3

    We are running mycom 23m and 250 vsd's the internediate side is where the issue is, oil temps are getting into the 103 f range and starting some carryover. sorry took so long to respond, Mike

  4. #4
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: floating head pressures-nh3

    What kind of oil cooling do you have? Thermosyphon, liquid injection....
    What did Hench tell you about this issue?

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: floating head pressures-nh3

    The fun envolved with saving a dollar on operating costs. Everyone forgets about system balances for the sake of efficiency.
    Spend a thousand dollars to save ten dollars.

  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: floating head pressures-nh3

    what is your oil type ?
    do have oil seperator after frist stage? does it works ? does oil retuning to comperssor?

  7. #7
    Join Date
    Jan 2010
    Location
    india
    Posts
    35
    Rep Power
    0

    Re: floating head pressures-nh3

    Dear all i have installed an new ammonia refrigeration system with priority vessel and de superheater. Now i m facing a problem that my pressure going to 16 bar and compressor get trip on high discharge pressure.i have also installed an temp transmitter in main discharge header but its temp goes upto 46 deg c.I have installed 2 Phe desuperheater and below the desuperheater 4 nos. phe condenser in parallel .I have taken condensers inlet tappings from bottom of de superheater outlet header. I have made an common condensate liquid header from condenser to Priority vessel. The height difference between condenser outlet bottom and condensate header top is 50 mm and condensate header bottom to liquid level in priority vessel is 1.2 mtr. I have given an vent line from priority vessel to desuperheater main inlet header. kindly give your valuable advise to resolve the high discharge pressure problem.

  8. #8
    Join Date
    Jan 2010
    Location
    india
    Posts
    35
    Rep Power
    0

    Post high discharge pressure problem in ammonia refrigeration system

    Dear all i have installed an new ammonia refrigeration system with priority vessel and de superheater. Now i m facing a problem that my pressure going to 16 bar and compressor get trip on high discharge pressure.i have also installed an temp transmitter in main discharge header but its temp goes upto 46 deg c.I have installed 2 Phe desuperheater and below the desuperheater 4 nos. phe condenser in parallel .I have taken condensers inlet tappings from bottom of de superheater outlet header. I have made an common condensate liquid header from condenser to Priority vessel. The height difference between condenser outlet bottom and condensate header top is 50 mm and condensate header bottom to liquid level in priority vessel is 1.2 mtr. I have given an vent line from priority vessel to desuperheater main inlet header. kindly give your valuable advise to resolve the high discharge pressure problem.

  9. #9
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: high discharge pressure problem in ammonia refrigeration system

    Quote Originally Posted by ghanghas85 View Post
    Dear all i have installed an new ammonia refrigeration system with priority vessel and de superheater. Now i m facing a problem that my pressure going to 16 bar and compressor get trip on high discharge pressure.....i kindly give (sic) your valuable advise to resolve the high discharge pressure problem.
    Ghang what means "priority vessel"; also check original design and installation docs and let us know your ideas based on it, without your modifications.
    Good Luck

  10. #10
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: floating head pressures-nh3

    Mike see my response in the other thread you started on the same subject.

    Ken