    York comprerssor



    Hello techs!!

    I recently received a call about a 3ph york compressor going out on thermal overload. One of the phases is pulling 60amps and other 2 are ok. The eng has done a phase rotation check and also mega the circuits and all is ok. Think the comp is on a chiller not sure though. sorry about lack of details Iv never heard of this fault and thought Id put it out there.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: York comprerssor

    Check and recheck all of the wiring, contactors etc.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: York comprerssor

    Check the supply side of things, the MCB, contactor etc., a faulty overload or contactor leg will give similar high current on one phase, loose terminals etc, etc. as Brian suggested double check everything up stream of compressor windings. The last straw is a mildly cooked winding, it will not show up with a multimeter but a high voltage meggar should nail it. Good luck.
    magoo

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: York comprerssor

    Hi COB
    Just a point to ensure you check the comp with a Mega and remove (if any) copper connection plates on the motor terminals. Also voltage or current imbalances. You could also Mega across each of the contactors. On one chiller we found a hot joint with a thermal scanner on a crimped cable end (bad crimp). Please let us know how you go and what you find on this one.

  5. #5
    yoleysi's Avatar
    yoleysi Guest

    Re: York comprerssor

    how to check an AA phase compressors