    w317chester's Avatar
    w317chester Guest
    Choosing a compressor
    Hello,
    I am trying to figure out what kind of compressor I need to use for my refrigeration system. The evaporator in my system is a counterflow concentric tube heat exchanger. In the outside tube will be water that I am trying to cool. In the inside tube, of course, is the refrigerant.
    Details of system:
    -water inlet temp: 22*C
    -desired water outlet temp: 3*C
    -mass flow rate of water: 0.1 kg/s
    -specific heat capacity water: 4210 J/kg*k
    And for a counterflow concentric tube heat exchanger:
    -q=(0.1 kg/s)(4210 J/kg*k)(22*C-3*C) = 8000 watts
    So I need to remove 8000 watts from the water for my desired flow rate and temps. How should I go about calculating and selecting the appropriate compressor for my system?
    Thanks.
    AND
    May 2006
    India
    74
    399
    Re: Choosing a compressor
    For comp selection , following data in to be stated
    cooling load : 8 kw
    refrigerant : ............ ?
    Evaporator temp : ......... ?? ( probaly ( - 2 ) deg c in your case
    system condensing temp : .......... ???????????
    Your comp vendor will select on the above info....... Again you need semi-hermetic / scroll etc to be specified
    d.d.koranne
    Sep 2003
    ISRAEL
    72
    4,248
    Your evaporating temp will be below 0°C, take that into consideration.
    You want to add Glycol to the water to avoid freezing, that will change the required cooling capacity.
    On the other hand, If you cant use Glycol, then you will have to add evaporator pressure regulator to avoid freezing. That might force you to use a larger evaporator and increase the water flow.
    Oct 2001
    Nottingham UK
    5,668
    Hey w317chester
    nice to see somone from the usa posting in Metric......
    As the other guys have said, you need to feed these details into your local compressor supply shop, they should be able to select for you.
    Do you have the other parts of your system already selected?