    Unknown Refrigerant



    Hi

    Is there anyway to determine the refrigerant in a system if the unit has no markings at all?

    thanks
    Shaun



  2. #2
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    235
    Rep Power
    15

    Re: Unknown Refrigerant

    Hi Shaun,

    in the markets there is already a device that analyses and/or identifies several gases. The amount of identified gases depends on the model (price). Very accurate, specially for pure products. "Ntron Analyzer"
    www.ntron.com
    Another thing to do is to take a sample and send it to a lab for a "chromatographic" inspection. (maybe this is not the correct expression, would appreciate your corrections)

    Regards,

    Nando.

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: Unknown Refrigerant

    It's complicated these days with drop ins and retrofits.
    In the old days, you just looked at the TX valve label.

    I suppose you could shut off the condenser and/or receiver section, run the condenser fan, check pressure, compare to ambient temp and look at charts?
    For a small system, just take it all out and start fresh is the best if you don't know.
    If hermetic compressor, expect oil hasn't been changed, so find out oil type from manufacturer to narrow down what refrigerant could be in it from the refrigerant pressure and what is compatible.

    For large systems where a refrigerant and oil change would be costly, then fri3Oils suggestion would be the way to go, but that wouldn't be cheap either.

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Unknown Refrigerant

    use a pt chart if the system still has liquid in it .check the model of the compressor

  5. #5
    Covi's Avatar
    Covi Guest

    Re: Unknown Refrigerant

    You can send the gas to a lab, they use a refractometer to measure the composition of the refigirant.

  6. #6
    Join Date
    Jul 2011
    Location
    United States of America
    Age
    59
    Posts
    86
    Rep Power
    13

    Re: Unknown Refrigerant

    The easiest way is to check the TXV and see what refrigerant it says. You can also see what the compressor is designed to use by checking literature on the compressor using the model number. You can narrow it down that way. If you really want to get scientific, vacuum out a recovery cylinder, recovering some of the liquid refrigerant into the cylinder then check ambient temp using a pres/temp chart to identify.

  7. #7
    Join Date
    Jun 2011
    Location
    United States
    Age
    36
    Posts
    9
    Rep Power
    0

    Re: Unknown Refrigerant

    That was really helpful. Thank you so much for sharing this information.
    _______________________
    Seo Marketing
    Marketing Seo

  8. #8
    Join Date
    Jan 2007
    Location
    USA
    Age
    58
    Posts
    145
    Rep Power
    18

    Re: Unknown Refrigerant

    how about hooking up a gauge where its saturated and looking at a pt chart.