    Air purger



    Hi,

    I want to ask you if you think is absolutely necessary an automatic air purger for an ammonia plant running -30/ + 35. At -30 C the pressure is around 1.2 bar, so no risk of air entering in the instalation.
    I think is no need for this air purger.

    What do you think?
    Thanks.



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Air purger

    It depends on how much do you want / could spend.

    Probably sometimes you will run at -35ºC, no? Or during some service always some air enter.

    However I confess that I wouldn't put it unless the Client wants it.
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Air purger

    Hi.
    your suction at 1.2 bar absolute is a bees **** above zero. So seriously concider an auto purger to keep system clean and tidy. Or else do a high side purge six monthly.

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Air purger

    Hi, Romanicus

    Quote Originally Posted by Romanicus View Post
    Hi,

    I want to ask you if you think is absolutely necessary an automatic air purger for an ammonia plant running -30/ + 35. At -30 C the pressure is around 1.2 bar, so no risk of air entering in the instalation.
    I think is no need for this air purger.

    What do you think?
    Thanks.
    No need for automatic purger (it will be better to have it, less headache regarding purging), but for sure you need to provide valves for proper manual purging from time to time ...

    One question, of course if you want to share that info with us ... which compressors you have installed, condenser/s etc.. ..... assume it is single stage plant ....

    Best regards, Josip
    Last edited by Josip; 29-03-2011 at 07:03 PM. Reason: add some text

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Feb 2006
    Location
    Romania
    Age
    49
    Posts
    17
    Rep Power
    0

    Re: Air purger

    Hi again, and thanks for the responses.

    No compressors yet installed.
    It's a tender book. I will go with 2 screws with economizer, VSD driven each, pumped ammonia, all evaporators with hot gas defrost, evaporative condenser.
    It's a logistic center. In the tender it's specified that you must have this automatic air purger, but i'm afraid that my competition will not offer it. I will offer it, because the tender asks for that, but i want to discuss with the client and maybe he will agree not to have it (if he pushes me with the price down)
    It's a one stage plant. I agree with you that it's nice to have an automatic air purger, but it costs quite a lot.
    For sure, if the client agrees not to have this automatic air purger i will install manual purging system.

    For Sandro: In normal operation is not possible to run at -35C. All the rooms are -20C rooms. BUT, the client might want to store ice cream or something like that, in this case, yes, it's possible to run at a lower suction temperature. But again, the tender specifies -28 evap, -20 air inlet in the evaporator.

    Till now the score is 3-1 against the automatic air purger

    All the best,
    Andrei

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Air purger

    Quote Originally Posted by Romanicus View Post
    Hi again, and thanks for the responses.

    No compressors yet installed.
    It's a tender book. I will go with 2 screws with economizer, VSD driven each, pumped ammonia, all evaporators with hot gas defrost, evaporative condenser.
    It's a logistic center. In the tender it's specified that you must have this automatic air purger, but i'm afraid that my competition will not offer it. I will offer it, because the tender asks for that, but i want to discuss with the client and maybe he will agree not to have it (if he pushes me with the price down)
    It's a one stage plant. I agree with you that it's nice to have an automatic air purger, but it costs quite a lot.
    For sure, if the client agrees not to have this automatic air purger i will install manual purging system.

    For Sandro: In normal operation is not possible to run at -35C. All the rooms are -20C rooms. BUT, the client might want to store ice cream or something like that, in this case, yes, it's possible to run at a lower suction temperature. But again, the tender specifies -28 evap, -20 air inlet in the evaporator.

    Till now the score is 3-1 against the automatic air purger

    All the best,
    Andrei
    My advice if you are in doubt: give the price for the air purger separated from the rest of the plant and let the Client decide.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    May 2007
    Location
    Pennsylvania
    Age
    51
    Posts
    113
    Rep Power
    17

    Re: Air purger

    Quote Originally Posted by Sandro Baptista View Post
    My advice if you are in doubt: give the price for the air purger separated from the rest of the plant and let the Client decide.
    Exactly right.

  8. #8
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Air purger

    Quote Originally Posted by Romanicus View Post
    Hi again, and thanks for the responses.

    No compressors yet installed.
    It's a tender book. I will go with 2 screws with economizer, VSD driven each, pumped ammonia, all evaporators with hot gas defrost, evaporative condenser.
    It's a logistic center. In the tender it's specified that you must have this automatic air purger, but i'm afraid that my competition will not offer it. I will offer it, because the tender asks for that, but i want to discuss with the client and maybe he will agree not to have it (if he pushes me with the price down)
    It's a one stage plant. I agree with you that it's nice to have an automatic air purger, but it costs quite a lot.
    For sure, if the client agrees not to have this automatic air purger i will install manual purging system.

    For Sandro: In normal operation is not possible to run at -35C. All the rooms are -20C rooms. BUT, the client might want to store ice cream or something like that, in this case, yes, it's possible to run at a lower suction temperature. But again, the tender specifies -28 evap, -20 air inlet in the evaporator.

    Till now the score is 3-1 against the automatic air purger

    All the best,
    Andrei
    You do not have to have one so that is 4 - 1 against, but

    Quote Originally Posted by Sandro Baptista View Post
    My advice if you are in doubt: give the price for the air purger separated from the rest of the plant and let the Client decide.
    Is very sound advice and that is what I would do.

    taz

    .

  9. #9
    Join Date
    Feb 2006
    Location
    Romania
    Age
    49
    Posts
    17
    Rep Power
    0

    Re: Air purger

    Thank you gentlemen. In the tender the air purger has a separate price, and so it will have in my offer. Thanks for the nice advices. Tommorow I have to issue the offer so keep the fingers cross for me
    Have a wonderful evening.

  10. #10
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Air purger

    Hope you can do the business unless you are from my competitor . Surely not my company only operate in Portugal.

    All the best