    Over charged system



    Hello friends, I know that an under charged system will cause the evaporator to freeze up. But is it possible for an over charged sytem to cause the evaporator to freeze up ? Thanks for your input.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Over charged system

    OVER CHARGE = Low superheat. Normal indoor heat exchanger TD. Higher than normal suction pressure, subcooling, head pressure & compressor current draw.
    Evaporator will freeze if you have evaporator fin temperature below 0°C. Rate of ice formation will depend on air flow and humidity, no matter if overcharged or not, if evaporator fin temperature is below 0°C.
    Since we expect higher suction pressure, ice formation could be somewhat lower in comparison with correctly charged system.
    Last edited by nike123; 26-03-2011 at 07:22 AM.

  3. #3
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Over charged system

    I wouldn't have thought the evaporator would freeze up because although having more refrigerant in it, it would be at the same or higher saturated temp/pressure therefore same or higher evaporator temperature.
    The only thing that might start freezing would be the suction line and compressor.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  4. #4
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Over charged system

    Tayters, a small capillary system will flood back with overcharge, well.. anything using cap really, but tx system overcharge (depends on how much % over it is), will still work as per normal untill Reciever fills up, then condenser backs up etc. BTW, time to get out of the dog house. The woofer wants its home back.. Mike.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Over charged system

    A faulty TX valve will create a frosted coil and system will appear overcharged, liquid stacked in high side

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Over charged system

    Hey Magoo, good point there! Wonder if origional poster meant frosted over partially, as in say 1/3 coil or fully.. In which case it may have nothing to do with gas charge. High heat load/humidity/lack of defrost time/too cold, etc.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Over charged system

    Hi Mikeref.
    With a full feed from TXV as in no distributor you can get the front face fully frosted, with a distributor generally get weird frost pattons on front face and through coil. Counter flow air to refrig of course.
    What should be flashing in evap is stacked in condenser.
    magoo

  8. #8
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Over charged system

    Quote Originally Posted by mikeref View Post
    Tayters, a small capillary system will flood back with overcharge, well.. anything using cap really, but tx system overcharge (depends on how much % over it is), will still work as per normal untill Reciever fills up, then condenser backs up etc. BTW, time to get out of the dog house. The woofer wants its home back.. Mike.
    Sorry Mike, I stand corrected. I had my blinkers on that day and had capillary in my mind when I wrote that. No other form of expansion device had entered into my thinking then.
    I remember blokes filling up supermarket packs with a good dollop of refrigerant when they couldn't find a leak and wanted it to last a while so it looked like it sprang another leak after they had repaired a leaky 'schrader'...

    Out the doghouse. Moved into the Sin Bin!

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  9. #9
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Over charged system

    think its easier to just remove the gas and recharge it,you know thats right then,if it persists then start looking into possible causes.

  10. #10
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Over charged system

    Hey Tayters, we all get thoes days, no drama though. Waiting to hear from OP, only been a few days. I see the doghouse is where you'll stay for now, couldn't stop laughing when i read your request for help today...Mike.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.