    Smile Very old cold store fan coil problem with pictures



    Hello

    These pictures are from an old cold store in a hotel, all the fan motors need to be re-wired and replaced.

    Someone has already had a go and there are a mixture of different fans blowing in both directions.

    I am going to supply and fit four new fans.

    Can anyone tell me which direction my fans should be blowing in?

    With similar units I have worked on previously the coil is facing the front and the air is drawn through the fan and out of the coil into the cold room.

    But this unit has the coil facing to the back so I am wondering if I should use an induced air fan so that the cold air is drawn over the coil first?

    Thanks
    Attached Images Attached Images



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Very old cold store fan coil problem with pictures

    In this construction, it looks to me that the fan blades pull the air and push it through the coil.

    Doe's the fins are about 5 to 8 mm apart? If so, I'm right.
    Also check where is the TEV or capillary entering the coil. The air should blow against the refrigerant flow.

  3. #3
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Very old cold store fan coil problem with pictures

    Thank you, the fins are less than 5mm apart maybe 3 or 4 mm and the TEV is just behind the motor on the right hand side but i'm not sure about flow. Good point though, i'd forgotten about that.

    Regards & thanks.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Very old cold store fan coil problem with pictures

    Check the refrigerant coil feed entries, normal is refrigerant flow through coil counter flow to air flow.

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Very old cold store fan coil problem with pictures

    Contactor, these motors look to be shaded pole and the blades should be very low pitch, so if replacing motors, make sure they are doing same revolutions. Air is sucked up and pushed through coil, as said above. larger motors may not fit due to limited space.. Mike.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Very old cold store fan coil problem with pictures

    To be honest, this evaporator isn't worth you spend a penny any longer on it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Very old cold store fan coil problem with pictures

    You need the small 5w round black fan motors

    http://www.remco.co.uk/products/33Range/page14.htm

    With new blades to suit. Air is drawn over the motor so make sure they are the correct rotation to do this. It may appear the evap has been fitted backwards -IE it blows against the back wall. This was very common years ago (BC - before cling-film) as it stops the cold air being blown directly onto the food and drying it out and blowing the air straight out the room when the door is opened..

  8. #8
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Very old cold store fan coil problem with pictures

    The refrigerant flow is towards the fans, so this is a forced air evaporator as advised - thanks.

    For the replacement fans, the existing ones are like this:

    http://www.remco.co.uk/products/24ra...ils.asp?id=261

    and one is the 5w round black one as described by r.bartlett in the post above.

    I've decided to use the 24 range motors because 3 of the the existing brackets will fit them and I can modify the other, I would need to get something made for the other motors which is not viable, unless anyone knows where I can buy some? (Not Remco).

    Do you think this will cause me a problem?

    I agree with you Peter_1 about replacing the whole unit, but I have a problem customer who has no brain.

    I also need to replace the fan guards, any ideas where I can buy them anyone, Remco can't help with these either.

    Thanks all.
    Last edited by Contactor; 26-03-2011 at 03:45 PM.

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Very old cold store fan coil problem with pictures

    Would something like this get over the mounting bracket and guard problem?

    http://www.remco.co.uk/products/fans/page24.htm

    Jon
    Mostly found in Oxfordshire, UK :)

  10. #10
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Very old cold store fan coil problem with pictures

    Crumbs yes it's older than I thought. Just ask any of the wholesalers for some 3w open wound fan motors and 4"blades (air over motor) to suit.
    Last edited by r.bartlett; 26-03-2011 at 08:15 PM.

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Very old cold store fan coil problem with pictures

    them coolers are bomb proof-they just last forever!!!