    I have to provide refrigeration system to cool flowing water (@1.6 GPM) from 90F to 46F in short time. I am wondering how to calculate the time it will take and the capacity of the unit I will need.
    Thanks.
    Auckland
    74
    3,357
    37
    Re: Flowing Water Cooling Rate and System Capacity
    A little bit more information could help. The statement "short time is not that exact ".
    TRIVEDIGB's Avatar
    TRIVEDIGB Guest
    Thanks Magoo.
    It is 25 minutes or less when ambient is 72F and 80 Minutes or less when ambient is 90F.
    Aug 2007
    Sydney
    52
    1,083
    23
    Hi TRIVEDIGB
    If you care to search this forum you will find detailed calculation for what you have asked.
    TRIVEDIGB's Avatar
    TRIVEDIGB Guest
    Tesla:
    I was not able to find.
    Split Croatia
    57
    6,151
    36
    Let see if I could give you some guidance on calculation.
    1,6 GPM in 25 min mean 1,6*25=40 gallons of water. That is around 180 kg of water.
    1 kg of water at 90°F (32,2°C) has specific enthalpy of 134 kj/kg
    1 kg of water at 46 (7,7) has specific enthalpy of 33 kj/kg
    To cool down 1 kg od water from 90°F to 46°F you need to remove 133-33=101 kj of heat.
    To cool down 180kg of water you need to remove 180*101= 18180 kj of heat which is around 5kWh of heat.
    To remove that heat in 25 min. time, you need cooling capacity of 60/25*5 = 12kW or 3,4TR
    Now you only need to ad to that heat gain in pipes and vessels where water circulate. If they are well insulated, 10% added capacity will probably do the job.
    Is this for cooling milk? Some other colleagues could add their practical advices from real life.
    TRIVEDIGB's Avatar
    TRIVEDIGB Guest
    Thanks a lot Nike123. Appreciated.
    May 2006
    India
    74
    399
    I guess it is UK gallon 1.6 / min
    BTU / HR
    USGPM = -------------------------
    500 X ( 90-46 )