    Flowing Water Cooling Rate and System Capacity



    I have to provide refrigeration system to cool flowing water (@1.6 GPM) from 90F to 46F in short time. I am wondering how to calculate the time it will take and the capacity of the unit I will need.

    Thanks.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Flowing Water Cooling Rate and System Capacity

    Hi
    A little bit more information could help. The statement "short time is not that exact ".

  3. #3
    TRIVEDIGB's Avatar
    TRIVEDIGB Guest

    Re: Flowing Water Cooling Rate and System Capacity

    Thanks Magoo.

    It is 25 minutes or less when ambient is 72F and 80 Minutes or less when ambient is 90F.

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Flowing Water Cooling Rate and System Capacity

    Hi TRIVEDIGB
    If you care to search this forum you will find detailed calculation for what you have asked.

  5. #5
    TRIVEDIGB's Avatar
    TRIVEDIGB Guest

    Re: Flowing Water Cooling Rate and System Capacity

    Tesla:

    I was not able to find.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Flowing Water Cooling Rate and System Capacity

    Let see if I could give you some guidance on calculation.
    1,6 GPM in 25 min mean 1,6*25=40 gallons of water. That is around 180 kg of water.
    1 kg of water at 90°F (32,2°C) has specific enthalpy of 134 kj/kg
    1 kg of water at 46 (7,7) has specific enthalpy of 33 kj/kg
    To cool down 1 kg od water from 90°F to 46°F you need to remove 133-33=101 kj of heat.
    To cool down 180kg of water you need to remove 180*101= 18180 kj of heat which is around 5kWh of heat.
    To remove that heat in 25 min. time, you need cooling capacity of 60/25*5 = 12kW or 3,4TR
    Now you only need to ad to that heat gain in pipes and vessels where water circulate. If they are well insulated, 10% added capacity will probably do the job.
    Is this for cooling milk? Some other colleagues could add their practical advices from real life.

  7. #7
    TRIVEDIGB's Avatar
    TRIVEDIGB Guest

    Re: Flowing Water Cooling Rate and System Capacity

    Thanks a lot Nike123. Appreciated.

  8. #8
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Flowing Water Cooling Rate and System Capacity

    I guess it is UK gallon 1.6 / min


    BTU / HR
    USGPM = -------------------------
    500 X ( 90-46 )

    1.9 X 500X 44 = 41800 BTU/ HR = 3.48 TR ................ WATER COOLING LOAD