I have to provide refrigeration system to cool flowing water (@1.6 GPM) from 90F to 46F in short time. I am wondering how to calculate the time it will take and the capacity of the unit I will need.
Thanks.
-
23-03-2011, 11:41 PM #2
Re: Flowing Water Cooling Rate and System Capacity
Hi
A little bit more information could help. The statement "short time is not that exact ".
-
24-03-2011, 07:20 PM #3
Re: Flowing Water Cooling Rate and System Capacity
Thanks Magoo.
It is 25 minutes or less when ambient is 72F and 80 Minutes or less when ambient is 90F.
-
25-03-2011, 08:59 AM #4
Re: Flowing Water Cooling Rate and System Capacity
Hi TRIVEDIGB
If you care to search this forum you will find detailed calculation for what you have asked.
-
25-03-2011, 03:26 PM #5
Re: Flowing Water Cooling Rate and System Capacity
Tesla:
I was not able to find.
-
26-03-2011, 04:24 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Flowing Water Cooling Rate and System Capacity
Let see if I could give you some guidance on calculation.
1,6 GPM in 25 min mean 1,6*25=40 gallons of water. That is around 180 kg of water.
1 kg of water at 90°F (32,2°C) has specific enthalpy of 134 kj/kg
1 kg of water at 46 (7,7) has specific enthalpy of 33 kj/kg
To cool down 1 kg od water from 90°F to 46°F you need to remove 133-33=101 kj of heat.
To cool down 180kg of water you need to remove 180*101= 18180 kj of heat which is around 5kWh of heat.
To remove that heat in 25 min. time, you need cooling capacity of 60/25*5 = 12kW or 3,4TR
Now you only need to ad to that heat gain in pipes and vessels where water circulate. If they are well insulated, 10% added capacity will probably do the job.
Is this for cooling milk? Some other colleagues could add their practical advices from real life.
-
29-03-2011, 08:12 PM #7
Re: Flowing Water Cooling Rate and System Capacity
Thanks a lot Nike123. Appreciated.
-
01-04-2011, 12:02 PM #8
Re: Flowing Water Cooling Rate and System Capacity
I guess it is UK gallon 1.6 / min
BTU / HR
USGPM = -------------------------
500 X ( 90-46 )
1.9 X 500X 44 = 41800 BTU/ HR = 3.48 TR ................ WATER COOLING LOAD