    NH3 pressure receivers' selection.



    Hello Guys,

    I'm looking for diagrams/methods to select pressure receivers (horizontal/vertical liquid separators, liquid receivers, oil receivers etc.) in the ammonia refrigeration installations. It would be also great, if you had the diagrams with SI units.

    I'm also interested in pipe diameter diagrams for ammonia installations.

    I've heard something that compressor manufacturers (Grasso, Gram, Stal, Sabroe, Frick) possess/possessed diagrams for pressure receivers and piping selection.

    Maybe someone from you could send me some diagrams, reference books etc.

    I would be grateful.

    Many, many thanks in advance for your assistance.

    Regards,

    Jacek



  2. #2
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: NH3 pressure receivers' selection.

    you can download Dircalc from Danfoss. This is excellent software for pipe sizing

  3. #3
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: NH3 pressure receivers' selection.

    Hello,

    what about pressure receivers?


    Quote Originally Posted by charlie n View Post
    you can download Dircalc from Danfoss. This is excellent software for pipe sizing

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: NH3 pressure receivers' selection.

    what you want to do ? built those or you want to chose right one

    in very brief writing
    In large system
    calculate your full load ( % 10 entry goods for each room)
    chose your compressor with adding safety factors-
    chose your condenser with adding safety factors

    calculate how much you need liquid refrigeration for each room in one hour
    about %30 of that is a your running time capacity for your pump ,chose your pump

    liquid receivers should have enough capacity to pump down your separators liquid to that.

  5. #5
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: NH3 pressure receivers' selection.

    Hi,

    Pressure receivers mean not only ammonia liquid receivers. It means also horizontal/vertical separators, intermediate-pressure vessels, oil receivers etc.

    Quote Originally Posted by mbc View Post
    what you want to do ? built those or you want to chose right one

    in very brief writing
    In large system
    calculate your full load ( % 10 entry goods for each room)
    chose your compressor with adding safety factors-
    chose your condenser with adding safety factors

    calculate how much you need liquid refrigeration for each room in one hour
    about %30 of that is a your running time capacity for your pump ,chose your pump

    liquid receivers should have enough capacity to pump down your separators liquid to that.