    marstair A/C cutting out on LP



    i am looking for help with a marstair A/C which has been cutting out on LP the system has pressure in the high side, the pressure on the low side rises and falls then cuts out on LP, the system has a internal expansion valve which has been changed twice any help would be much appreciated thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: marstair A/C cutting out on LP

    ...system has pressure in the high side...
    Yes, but does it have enough?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: marstair A/C cutting out on LP

    Could it have moisture in the system? Does it have a filter drier and sight glass? Also what Brian said
    Last edited by monkey spanners; 19-03-2011 at 02:25 PM. Reason: de do do do, de da da da
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Mar 2011
    Location
    england
    Age
    34
    Posts
    101
    Rep Power
    14

    Re: marstair A/C cutting out on LP

    yea ther is plenty of refrigerant in the system as it was reclaimed to leave pressure in th system it has a filter drier and sight glass which has been changed when the system has been worked the only thing that has not been done is triple vac

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: marstair A/C cutting out on LP

    No evacuation ???
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Mar 2011
    Location
    england
    Age
    34
    Posts
    101
    Rep Power
    14

    Re: marstair A/C cutting out on LP

    yea system was vacuumed to 1torr and works for so long then works itself again.

  7. #7
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: marstair A/C cutting out on LP

    I was gonna say a blocked capilary but I thought I would leave it to the more advanced guys to answer

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: marstair A/C cutting out on LP

    What does the oil look like? Had an old hitachi or tosh unit (forget which) that the oil had gone brown and nasty, system would work ok then kind of pump down, was told it way due to the oil going lumpy in strainers (or similar but more technical sounding reason), once it had warmed up, normal service resumed for a while.
    Chucked system in skip and put new one in, fixed!
    Mostly found in Oxfordshire, UK :)

  9. #9
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: marstair A/C cutting out on LP

    Ok so the TEV has been changed twice !Why??
    At what back pressure is it tripping the lp switch ,and at what pressure does the manufacturer say it should trip the lp switch,(is it adjustable) is there a preset lp delay on start up via control circuit or pcb?.
    If the lp switch is bridged out how does it run ? or does it pumpdown ?
    Is the bulb/phial mounted correctly and insulated correctly.
    What are the operating conditions indoor / outdoor.
    The more info you can give the better.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  10. #10
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: marstair A/C cutting out on LP

    firstly is the a moisture indicator on the sightglass (yellow/green)this tells you if the system has moisture in,if it has not got one in fit one with a biger liquid line drier ,085 or larger,vac out and recharge with new refrigerant,the old may be contaminated.

  11. #11
    Join Date
    Mar 2011
    Location
    england
    Age
    34
    Posts
    101
    Rep Power
    14

    Re: marstair A/C cutting out on LP

    will try that thanks for the help i will keep you informed and let you know how it goes

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: marstair A/C cutting out on LP

    Check the evap fan/air flow too, if it stops then the tev will shut down to maintain superheat, it could shut enough to trip the lp switch.
    Mostly found in Oxfordshire, UK :)