    Question Measure suction line pressure drop with thermometer



    I was on a job site a 20 ton split system and an engineer took a temperature reading at the suction outlet of the evaporator and another temperature reading at the suction inlet of the condensing unit.

    He then declared that the pressure drop was OK.

    How did he do that with no liquid refrigerant present in the suction lone?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Measure suction line pressure drop with thermometer

    Hi Steve,
    A good practise would be to measure pressure and temperature and check that it matches.

    He must be a magician

    Chemi

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Measure suction line pressure drop with thermometer

    Hi Steve,

    I can only guess at what this person was doing. Here is one:

    1) He was converting the two temperatures to the saturation pressures at both locations and assuming the difference in pressure was due to the suction line piping.

    This would have to be based on more rules of thumb and assumptions to determine the pressure loss than I care to imagine.

    If he was looking for liquid refrigerant in a system, would he use a "divining" rod? (Sorry, I could not resist that comment)

    I would have rather seen him estimate pressure drop by using the unit capacity and referencing a pipe pressure loss chart for the refrigerant used, pipe size, and refrigerant.

    I'm not sure how much this helps you, but this is my best guess.

    Regards,
    US Iceman

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Measure suction line pressure drop with thermometer

    Quote Originally Posted by US Iceman

    He was converting the two temperatures to the saturation pressures at both locations and assuming the difference in pressure was due to the suction line piping.

    This would have to be based on more rules of thumb and assumptions to determine the pressure loss than I care to imagine.

    I came to that conclusion. There may have been a confusion in methodologies. It's certainly an unreliable way of estimating pressure loss.

    As I recall some of the old text books, suction lines were sized on a pressure loss usually given as the equivalent pressure to less than 2 deg F. (1 deg C) in most instances.

    The problem with measuring temperatures along lengths of pipes is that you don't know how much heat is picked up en route.

    The only reliable way to measure pressure in my estimation is with a gauge or manometer.

    .
    ________
    Jean Behra
    Last edited by Argus; 07-02-2011 at 08:30 AM.

  5. #5
    Join Date
    Dec 2003
    Location
    uk
    Age
    51
    Posts
    62
    Rep Power
    21

    Re: Measure suction line pressure drop with thermometer

    I agree with above, He was just converting temp to presure and asuming increase in temp was convertable to presure increase, But not taking into acount temp picked up along the way as Argus mentioned.

    Im just wondering why was he looking to measure the presure loss, All suction lines will have some amount of presure loss as will the liquid line and any pipe in the system, Why was he measuring the loss, was there a problem with the system,

    Just wondering

  6. #6
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Measure suction line pressure drop with thermometer

    Quote Originally Posted by chilly

    Why was he measuring the loss, was there a problem with the system,

    Just wondering

    If he was carrying out a survey, or acting as a consultant, it's part of the brief: it's called 'Justify the Fees'

    .
    ________
    glass pipes
    Last edited by Argus; 07-02-2011 at 08:30 AM.

  7. #7
    Join Date
    Sep 2005
    Location
    Atlanta Georgia USA
    Age
    69
    Posts
    80
    Rep Power
    19

    Re: Measure suction line pressure drop with thermometer

    To All

    He was checking for undersized lines or crimps. I think line size was 21/8".

    This guy is a seasoned professional engineer. There were various groups involved(owner, architect, factory, installing contractor, and me the after fact consultant to installing contractor). This guy represented the factory and is really a good engineer.

    What he was saying validates proper installation by my customer so I Didn't want to ask too many questions and throw water on the party.

    The problem ended up being mis applied equipment.

    Steve

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Measure suction line pressure drop with thermometer

    Hi Steve,

    This almost sounds like the typical architect selection for refrigeration systems. 20 Ton condensing unit requires 20 Ton evaporator capacity. Good for any temperature.

    I have seen this happen several times, and in every case problems were the result.

    For anyone reading this, please don't take this seriously as a method to select refrigeration equipment and expect it to work. Components must be carefully selected for the exact operating conditions.

    It sounds like this was a finger pointing contest. Not too much fun....

    Can you share the nature of the problem Steve?

    Regards,
    US Iceman
    Last edited by US Iceman; 17-09-2005 at 11:06 PM. Reason: editing

Similar Threads

  1. pressure drop of pump return line ammonia
    By Moeller in forum Fundamentals
    Replies: 5
    Last Post: 04-09-2007, 05:21 AM
  2. propane compressor suction drum
    By Ahmed_LNG in forum Refrigerants
    Replies: 7
    Last Post: 01-01-2006, 08:01 AM
  3. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  4. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •