    Hussman rack



    I am just starting to work on supermarket racks and am having a problem with the low temp side of it. The suction pressure is running about 10 psig higher then it should, the medium temp side is running pretty much right on. All the temperatures are holding at steady and are fine. We have recently had a large leak in the system and it has been reparied. Also have replaced 2 txv's in two freezers, the refrigerant is 507. Wondering if someone could guide me in the right direction. If you need any more info let me know

    Thanks



  2. #2
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Hussman rack

    try pump testing the compressors, you may have a valve passing across the head!!

  3. #3
    Join Date
    Oct 2006
    Location
    united kingdom
    Age
    55
    Posts
    65
    Rep Power
    19

    Re: Hussman rack

    Hi Jsw,

    Is this hussmann pack a compound pack, were ht discharge dumps into Low temp suction and discharge gas is cooled via the teat valve?

    Cheers

    Supermarketguy

  4. #4
    Join Date
    Mar 2011
    Location
    canada
    Posts
    9
    Rep Power
    0

    Re: Hussman rack

    No it is not. 3 compressors on the med temp side and 2 on the low temp side connected in parallel. The system has a surge reciever/vavle, an Parker A8 holdback valve, a parker A9 press regulator, heat reclaim valve, epr valves,etc.