    water flow measurement on stad valve



    Hi evryone.Ive been recording water flow on stad valve last week when adjusting the valve on shut position the meter said error pressure too large.when i open the valve the meter said to small pressure.Anyone come across that before.



  2. #2
    Join Date
    Jan 2010
    Location
    australia
    Age
    39
    Posts
    32
    Rep Power
    0

    Re: water flow measurement on stad valve

    stad valve on return? if you close valve will measure high back pressure. then when open could measure low flow for number of reasons pumps etc for correct measurement dont you want the stad valve open? whats it for condenser water?

  3. #3
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: water flow measurement on stad valve

    Its on the fan coil unit on return.its just i cannot get a reading on some of them.to low or to large when open or shut.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: water flow measurement on stad valve

    With the valve closed any readings taken are pointless, no flow is happening across the orifice.

    When open if you do not have a sensible reading then you should check that the valves have been correctly sized and correctly positioned.
    Brian - Newton Abbot, Devon, UK