    Cold Room Air Circulation Rates



    Hello!!!

    Is there a ASHRAE recommendation about how many air changes per hour must be in a determinated Cold Food Storage room???

    I've seen some tables from some refrigeration compressors/evaporators manufacturers (ex.BOHN) that recommends you a minimum air changes per hour, but I can't found the base of that recommendation, is that taken from ASHRAE???

    Thank you!



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: ASHRAE Recommendation Air Changes/Hour

    Why would you change air in cold room if, for example, food is frozen and packed in vacuum packing.
    If you mean air circulation rate in cold room, than that is totally different from what you mean by air changes.

  3. #3
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: ASHRAE Recommendation Air Changes/Hour

    Thanks nike132, that's the correct word for what I was trying to refer for.

    Can you tell me how can I change the subject of the thread, or just the moderators can???

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Cold Room Air Infiltration Rates

    Done......

  5. #5
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Cold Room Air Infiltration Rates

    Thanks Frank, but I meant that "Air Circulation Rate" was the correct word for what I was looking for. Could you change the "Infiltration" for "Circulation" in the subject please???

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Cold Room Air Infiltration Rates

    The air circulation rate would just be the amount of air pushed around by the evap fan. Is this the information you need?

  7. #7
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Cold Room Air Infiltration Rates

    Yes, that's why I'm looking for. This is what I found on Heatcraft-BOHN engineering manual:

    4. Type of Operation/Air Flow
    Two important considerations in the selection and location of the unit cooler are uniform air distribution and air velocities which are compatible with the particular application.
    The direction of the air and air throw should be such that there is movement of air where there is a heat gain; this applies to the room walls and ceiling as well as the product. The unit cooler(s) should be arranged to direct its discharge air at any doors or openings, if it all possible. Avoid placing the unit cooler in a position close to a door where it may induce additional infiltration in to the room; this can cause fan icing and a condition known as hoar-frost. Also, avoid placing a unit in the air stream of another unit, because defrosting difficulties can result.
    For general storage coolers and holding freezers, there are not criteria for air velocities within the room. The total supply of air is such that approximately 40 to 80 air changes occur each hour. This is an air conditioning term which is calculated as follows:
    Air Changes = (total cfm*) x 60
    internal room volume
    * includes all unit coolers and auxiliary fans
    This equation disregards the air motion which is induced by the discharge air from the unit cooler. For simplicity, the gross volume of the room is used unless the product and equipment occupy more than 10% of the volume. Specific applications such as cutting rooms and banana ripening rooms have desired limits. The table below indicates the minimum and maximum quantities of air for particular applications. Recommended Air Changes/Hour: (here is the table)

    This is regarding the Evaporator(s) selection criteria. Heatcraft says that you should select an evaporator which gives enough CFM so the air changes/hour is the recommended on the table.
    Last edited by georgedvf; 11-03-2011 at 09:45 PM.

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Cold Room Air Circulation Rates

    Evaporator air circulation rates are determined by the evapoartor manufacture for a given performance factor. Generally from my experience somewhat inflated, air volume to performance that is to say.

  9. #9
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Cold Room Air Circulation Rates

    Major reason of air circulation to prevent hot spots in the freezer. Some old style freezers don't have air circulation at all. A while ago I saw freezer that had brine cooled by ammonia. In the freezer brine piping was on the walls and under the ceiling. No forced air circulation, but only natural convection.

  10. #10
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: Cold Room Air Circulation Rates

    Hi there,

    you always end up with more CFM than this table gives you. This is just an indication.

    Lets try this : a holding freezer with 10m x 10m x 3m = 300 m³ = 10594 ft³
    Using the equation with maximum air change 80 = 80=CFMx60/10594 CFM = 14125
    For this room you would need at least two evaporators for good air circulation. When you select from the catalog then you will see that in total you have more CFM than 14125.

    Cheers
    Even Einstein Asked Questions

  11. #11
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Cold Room Air Circulation Rates

    When small rooms that's true, you always end up with more CFM than those that the table indicates.

    But when the room is big, it is when I can't reach the air changes that the table indicates, I'm talking about rooms of 200,000 ft³. For example for a Holding Freezer application tha table says minimun 40 air changes/hour but the maximum I got with standar evaporators is 12 air changes/hour.
    Last edited by georgedvf; 14-03-2011 at 06:15 PM.

  12. #12
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Cold Room Air Circulation Rates

    Does anyone has reference for this from ASHRAE or somewhere else????

  13. #13
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Cold Room Air Circulation Rates

    Circulations rates depend on the product stored, prefrozen, unfrozen, chilled what ever and a thousand other criteria items, traffic values, respiration rates, the list goes on and on.
    Join ASHRAE and pay for manuals and be totally confused at the end of it.
    My favourate saying is ASHRAE jockeys design the perfect system that never works. Design comes from practical experience and understanding your clients ACTUAL needs. Then apply all the experience and deliver the system that does operate efficiently and with in clients requirements.

    Grumpy

  14. #14
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Cold Room Air Circulation Rates

    I'll be glad if some other reference besides ASHRAE is presented. It's just that I've not seen another reference about this subject.

    So nobody has any reference???

  15. #15
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Cold Room Air Circulation Rates

    Hi, georgedvf

    Quote Originally Posted by georgedvf View Post
    When small rooms that's true, you always end up with more CFM than those that the table indicates.

    But when the room is big, it is when I can't reach the air changes that the table indicates, I'm talking about rooms of 200,000 ft³. For example for a Holding Freezer application tha table says minimun 40 air changes/hour but the maximum I got with standar evaporators is 12 air changes/hour.
    For storage room/s (goods are at temperature) must be enough 20-40 air changes per hour - practical experience .... for process rooms for cooling or freezing of some goods there are other methods for calculation of cooler/s and fans ...

    I assume, your room is about 90x90x25 ft, so you can utilize about 85% of your floor area and about 90% of your room height (for smaller rooms factor is smaller) ... i.e. from your 200000 [ft³] occupied is about 150000 [ft³] 200000x0,85x0,90 = 153000 [ft³] ... so you have 50000 [ft³] of air to circulate around ....

    .. from your calculation (if I'm not wrong 12changes/h x 200000[ft³] = 2400000[ft³/h]/50000[ft³]=48 changes/hour with full room occupied and coming down when room is less occupied ...

    I agree with Magoo ... there is a lot of criteria items having effect on circulation rate i.e cold room calculation and construction ... the biggest problem are our clients ... wanted always bigger room/s with very strong cooler/s (to be there just in case if they need it one day) and then keep it partially empty 8 months per year, accusing vendors for high electricity bills... so we need to find out what are real needs of our client and then deliver exactly that ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  16. #16
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Cold Room Air Circulation Rates

    I have one cold Room Manual & it has a chart for air circulation rates.
    Type of application Minimum Maximum
    Holding Freezer : 40 80
    Packaged Holding Center 40 80
    Meat Chill Room 80 120
    Banana Ripening 120 200
    Veg/ Fruit Storage 30 60
    Blast Freezer 150 300
    Work areas 20 30
    Unpacked Meat Storage 30 60
    Air Changes = Total CFM of air cooler x 80 / ( internal Cold room Volume)
    Last edited by smpsmp45; 25-03-2011 at 07:27 AM.

  17. #17
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Cold Room Air Circulation Rates

    smpsmp45: is this the heatcraft manual??? It's almost the same, only the Cutting Room is missing.

  18. #18
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Cold Room Air Circulation Rates

    This we got from cold room manual prepared by Erricson India

  19. #19
    RG-NH3's Avatar
    RG-NH3 Guest

    Re: Cold Room Air Circulation Rates

    SMPSMP45: Could you give us where we can download the document?