If the inside temp is 10 deg C the indoor coil frosts on cooling yet if on heating the outside temp is 10C then the outdoor coil doesn't tend to?
What's the difference -air volume perhaps?Last edited by r.bartlett; 11-03-2011 at 02:33 PM.
-
11-03-2011, 06:54 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Frosting
Difference is TD of heat exchangers. TD, among others, depend on air/water flow.
-
11-03-2011, 07:43 PM #3
Re: Frosting
The frost is water vapour condensating on the cold coil, so it is not just about temperatures. You have to look at the humidity factor as well. DB/WB.