    aspera compressor fault



    Recently went to a chiller running on r404a. Compressor trying to start then failing. Compressor pullin 16A. Windings did not add up so replaced compressor. System fired up ok ran for about 15min then back to same fault as old compressor. All electrics where changed also.

    Anybody came accross this issue before or had the same fault?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: aspera compressor fault

    Compressor model?

    Do you have any power supply problems at all?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: aspera compressor fault

    whats comp size ... fla... sizeof cab

  4. #4
    Join Date
    May 2008
    Location
    Belgie
    Posts
    13
    Rep Power
    0

    Re: aspera compressor fault

    Is de spanning nog goed 400 v of 230v ezv?
    Is er koelwater of doorstroming in de condensor?
    Kan hij zijn warmte afgeven?
    Heeft de compressor nog gedraaid juist voor je er was?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: aspera compressor fault

    Quote Originally Posted by Aper Willy View Post
    Is de spanning nog goed 400 v of 230v ezv?
    Is er koelwater of doorstroming in de condensor?
    Kan hij zijn warmte afgeven?
    Heeft de compressor nog gedraaid juist voor je er was?
    {Translation}
    If the voltage is still 400 v or 230v ezv?
    Is cooling water or flow into the condenser?
    Can he have heat?
    If the compressor is still running just before you were there?
    +
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: aspera compressor fault

    The model was NJ9232GK. Just before the fault the back pressure droped almost into a vac I thaught chiller had reached temp but controller still asking for compressor. Then back to same fault when i retested the windings on new comp they did not add up.. Gulp.....

  7. #7
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: aspera compressor fault

    good translation brian and quick you would have been usefull on a set of decks we fitted with italian wiring and itialian commisioning ticket

  8. #8
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: aspera compressor fault

    Comp is a 230v running on R404a. If by flow you mean refrigerant? Compressor only to hot to touch after fault recurred. Head pressure was 250psi but I reduces this to 200 with fan speed controller. Back pressure was 30/40 psi, before fault.

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: aspera compressor fault

    blocked capillary or expansion valve,causing the compressor to go out on klixxon!

  10. #10
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: aspera compressor fault

    I blew lines through with ofn before pressure test to ensure no blockages. Also monitered head pressure guage and vacced through low side for it pulling. All ok system has pressure switches installed so it would have stoped on high pressure if blocked. Back pressure did drop rapidlay thats why i thaught solanoid had de enirgized but it hadnt.

  11. #11
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: aspera compressor fault

    Cut the original comp open and see what has gone wrong with it, may point you to what is wrong now.
    Mostly found in Oxfordshire, UK :)

  12. #12
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: aspera compressor fault

    Strange to have low pressure drop and compressor stall as well. I'm thinking there is power supply problems. Sticking my neck out... solenoid looses full voltage and valve closes then low voltage drops compressor out as well.??
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: aspera compressor fault

    First, you should measure voltage at compressor terminals with instrument which has min/max function until error is repeated and see if MIN voltage is lower than 187V. If yes, you have power supply problem or some component in series with compressor power supply is faulty.
    If not, than you should measure current and pressures and if they are matching with data given here:
    http://www.embraco.com/DesktopModule...943NA01_ig.pdf

  14. #14
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: aspera compressor fault

    Thanks for tip and download document I will try that. Having a think about it today I think solenoid valve must have deenirgised due to temp in chiller. This is what has caused pressure to drop and compressor has then failed on start up.

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: aspera compressor fault

    Is this pump down system? Where is solenoid placed? How many pressure controls you have?

  16. #16
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: aspera compressor fault

    Is it a high starting torque compressor?
    Mostly found in Oxfordshire, UK :)

  17. #17
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: aspera compressor fault

    have you tried bench testing the old comp to see if it runs when not on unit.... will give u a beter idea if the comp is faulty or it is the system its on

  18. #18
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: aspera compressor fault

    The comp is a high torque comp which starts using a 90uf cap. It has a duel pressure switch low side is set for 18psi and high side was 400psi I cant rem what diff was set for. Solenoid valve has been mounted right next to evap and the run is approx 10m. I don't have the facility to bench test but was thinking of getting a comp analyzer to see if it can start comp. Has any one got experience with one are they any good?

  19. #19
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: aspera compressor fault

    all you need is to wire live and neutral onto the comp electrics..... do it anywere

  20. #20
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: aspera compressor fault

    didnt think you could test the comp like this as it req a high kick start cap. I will try it and see thanks for the tip. How long could i leave it before the poss of damage or ware. Say 5 min?

  21. #21
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: aspera compressor fault

    hi
    did you change filter drier.surely you have a restriction causes compressor failure to restart.you can check if there is a restriction when compressor pull into vac.i wonder compressor should stop you said low side is set to 18 psi.you can check your lhp & system components dirty condenser blocked drier dirty expansion valve screen.hope that help

  22. #22
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: aspera compressor fault

    hi
    yes dryer was changed defo no restrictions in system. When i go back i will run a straight feed to the compressor independently from control circuit and see if it starts. Its just strange that it failed on restart comp was just clicking wanting to go. My thoughts are that windings have failed but this is very uncommon on a new comp. Plus to have the same fault as one removed. STRANGE! I'm 90% certain that power in circuit is OK I tested it but did not monitor it over a period of time.

  23. #23
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: aspera compressor fault

    Hi all
    Thaught i would keep post updated. Decided to change comp as suspect windings failure. New compressor started first time and currently running away nicely. Old compressor failed after first or second restart. Will give it a couple of days and see how it goes.

  24. #24
    farrefriger's Avatar
    farrefriger Guest

    Re: aspera compressor fault

    by any chance were the compressor electrics
    box laying flat when this happened two the frist compessor

  25. #25
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: aspera compressor fault

    Hi
    No not the first compressor that we condemned but the one that was changed where.
    Could that have been an issue?

  26. #26
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    16

    Re: aspera compressor fault

    If you suspect a compressor burn out, install a suction line drier just upstream of the compressor, allways quote the customer the cost of returning to site to remove the drier....

  27. #27
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: aspera compressor fault

    if the electrics were lyin flat then theres always a chance that the relay wont change from start to run therefore going out on clixen