    compliments
    any body know the basic equation for desiding the flow rate of the chilled water pump with respect of the size of evaporator in tons
    thanks
    Sep 2004
    Dubai - United Arab Emirates
    44
    Re: chilled water pump design
    Dear Afif,,
    afif the flow rate of a chilled water system is related to the tonnage, first you have to transform the tonnage to KW, i.e. 1 Ton = 3.41 KW, then you can apply this formula:
    Q= m x Cp x DT
    Q: Capaciy in KW
    m: Flow rate (Kg/sec)
    Cp: Specific Heat (For Water 4.18 KW/Kg.K)
    Dt: Delta T (entering - leaving chiller water temp)
    then u'll get your flow rate man ..
    Oct 2003
    5,630
    Jun 2005
    Madison
    61
    32
    Quote Originally Posted by Mahmoud
    Dear Afif,,
    Q= m x Cp x DT
    Q: Capaciy in KW
    1 ton = 12000 Btu/hr = 3.5168528421 KW
    5,667
    Specific heat of water = 4.19kj/kg.K
    kj/s = kw
    Dec 2004
    LEBANON
    44
    854
    Hi guys
    Afeef take care man , if you are using glycol or other antifreezing agent the specific heat of the blend changes .
    Best regards