    chilled water pump design



    compliments
    any body know the basic equation for desiding the flow rate of the chilled water pump with respect of the size of evaporator in tons
    thanks



  2. #2
    Join Date
    Sep 2004
    Location
    Dubai - United Arab Emirates
    Age
    44
    Posts
    37
    Rep Power
    0

    Re: chilled water pump design

    Dear Afif,,

    afif the flow rate of a chilled water system is related to the tonnage, first you have to transform the tonnage to KW, i.e. 1 Ton = 3.41 KW, then you can apply this formula:

    Q= m x Cp x DT

    Q: Capaciy in KW
    m: Flow rate (Kg/sec)
    Cp: Specific Heat (For Water 4.18 KW/Kg.K)
    Dt: Delta T (entering - leaving chiller water temp)

    then u'll get your flow rate man ..

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: chilled water pump design

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Jun 2005
    Location
    Madison
    Age
    61
    Posts
    32
    Rep Power
    0

    Re: chilled water pump design

    Quote Originally Posted by Mahmoud
    Dear Afif,,

    afif the flow rate of a chilled water system is related to the tonnage, first you have to transform the tonnage to KW, i.e. 1 Ton = 3.41 KW, then you can apply this formula:

    Q= m x Cp x DT

    Q: Capaciy in KW
    m: Flow rate (Kg/sec)
    Cp: Specific Heat (For Water 4.18 KW/Kg.K)
    Dt: Delta T (entering - leaving chiller water temp)

    then u'll get your flow rate man ..
    1 ton = 12000 Btu/hr = 3.5168528421 KW

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: chilled water pump design

    Specific heat of water = 4.19kj/kg.K

    kj/s = kw

  6. #6
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: chilled water pump design

    Hi guys


    Afeef take care man , if you are using glycol or other antifreezing agent the specific heat of the blend changes .

    Best regards
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

Similar Threads

  1. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  2. Homemade Heat pump water heater
    By busman in forum Technical Discussions
    Replies: 20
    Last Post: 05-02-2008, 04:04 PM
  3. VFD heat pump water heater?
    By star882 in forum New Technologies
    Replies: 0
    Last Post: 23-05-2006, 08:36 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. chilled water PHE
    By priti in forum Trouble Shooting
    Replies: 1
    Last Post: 31-07-2002, 08:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •