compliments
any body know the basic equation for desiding the flow rate of the chilled water pump with respect of the size of evaporator in tons
thanks
-
14-09-2005, 11:28 AM #2
Re: chilled water pump design
Dear Afif,,
afif the flow rate of a chilled water system is related to the tonnage, first you have to transform the tonnage to KW, i.e. 1 Ton = 3.41 KW, then you can apply this formula:
Q= m x Cp x DT
Q: Capaciy in KW
m: Flow rate (Kg/sec)
Cp: Specific Heat (For Water 4.18 KW/Kg.K)
Dt: Delta T (entering - leaving chiller water temp)
then u'll get your flow rate man ..
-
14-09-2005, 06:59 PM #3
Re: chilled water pump design
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
15-09-2005, 01:57 PM #4
Re: chilled water pump design
Originally Posted by Mahmoud
-
15-09-2005, 08:11 PM #5
Re: chilled water pump design
Specific heat of water = 4.19kj/kg.K
kj/s = kw
-
16-09-2005, 12:06 AM #6
Re: chilled water pump design
Hi guys
Afeef take care man , if you are using glycol or other antifreezing agent the specific heat of the blend changes .
Best regardsEngineering, sciences, math, physics and my brain will generate "not responding " soon
Similar Threads
-
pure water from air
By Lc_shi in forum New TechnologiesReplies: 32Last Post: 26-02-2009, 12:25 PM -
Homemade Heat pump water heater
By busman in forum Technical DiscussionsReplies: 20Last Post: 05-02-2008, 04:04 PM -
VFD heat pump water heater?
By star882 in forum New TechnologiesReplies: 0Last Post: 23-05-2006, 08:36 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM -
chilled water PHE
By priti in forum Trouble ShootingReplies: 1Last Post: 31-07-2002, 08:25 PM