  1. #1
    eugene82's Avatar
    eugene82 Guest

    help



    Hi I am installing a heat pump my pressures seam to be out of the norm, the outside air is 41F the low side pressure is 104psi and the high side is 450psi can this be my txv outside or my system is overcharged?



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: help

    Hey Eugene,

    What refrigerant is the system running?

    Is it a new instal or an existing system that has developed a fault, if so any history?

    Any superheat and subcooling readings?

    Cheers Jon
    Mostly found in Oxfordshire, UK :)

  3. #3
    eugene82's Avatar
    eugene82 Guest

    Re: help

    its r410A, the system is new i am about to do the subcooling reading

  4. #4
    eugene82's Avatar
    eugene82 Guest

    Re: help

    the outside unit came pre-charged so when you weld the pipes and vacuum then you just open the valves on the outside unit that's why i don't know how much r410A is inside.

  5. #5
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: help

    these pressures are around the norm for 410a it is a higher pressure refrigerant, check your temp difference accross your coil in cooling should be 10-12 degrees C if so then you dont have a problem make sure all your coils and filters are clean also

  6. #6
    eugene82's Avatar
    eugene82 Guest

    Re: help

    thanks, it was my air flow it was not enough its working fine now i've up the speed of the fan