    HC-22a VS R-22



    Hi all. i would like to get some info from you guys, regarding on these 2 refrigerant. Recently my company asked me to find the COP for these 2 refrigerants. HC-22a will be a drop-in replacement for R-22a as the supplier proposed to the company. How do i calculate COP for the chiller based on these 2 refrigerant? Please help as i'm really new to this refrigeration system..



  2. #2
    GOPINATH's Avatar
    GOPINATH Guest

    Re: HC-22a VS R-22

    Hi Hello,

    Iam going to Retrofitt R290 in R22 split air conditioner of capacity 18000 Btu,for performance testing , with no modification in the system , is there any leak testing alarm devices available to sense the leakage in the system , The system is tested in a closed psychrometric room at various conditions.

    Regards,
    Gopinath.
    +91 9884783674

  3. #3
    Join Date
    Mar 2011
    Location
    Malaysia
    Age
    37
    Posts
    9
    Rep Power
    0

    Re: HC-22a VS R-22

    u r not answering the question. u just added another one. and it does not correlate at all.

  4. #4
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: HC-22a VS R-22

    Simply stated, COP = (useful refrigeration) / (net work).

    The COP of a simple Carnot cycle can be stated as:

    COP = (T1(s1-s4)) / ((T2-T1)(s1-s4))

    COP = T1 / (T2-T1)

    s = entropy (BTU/ (lb)(degree Rankin)
    T = temperature (rankin)

    Ken
    Last edited by TXiceman; 09-03-2011 at 12:28 PM.

  5. #5
    Join Date
    Mar 2011
    Location
    Malaysia
    Age
    37
    Posts
    9
    Rep Power
    0

    Re: HC-22a VS R-22

    Quote Originally Posted by TXiceman View Post
    Simply stated, COP = (useful refrigeration) / (net work).

    The COP of a simple Carnot cycle can be stated as:

    COP = (T1(s1-s4)) / ((T2-T1)(s1-s2))

    s = entropy (BTU/ (lb)(degree Rankin)
    T = temperature (rankin)

    Ken
    Hi Ken.
    Thanks a lot. Correct me if i'm wrong, but s1 is entropy at T1 and s2 is entropy at T2 right? how about s4? What does it represent?

    tQ for your co-operation!

  6. #6
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: HC-22a VS R-22

    I had to correct my formula...fat fingers and a slow brain.

    T3 = T2
    and T4 = T1

    Refer to Refriferation and Air Conditioning by W.F. Stoecker

    Ken

  7. #7
    Join Date
    Mar 2011
    Location
    Malaysia
    Age
    37
    Posts
    9
    Rep Power
    0

    Re: HC-22a VS R-22

    Quote Originally Posted by TXiceman View Post
    I had to correct my formula...fat fingers and a slow brain.

    T3 = T2
    and T4 = T1

    Refer to Refriferation and Air Conditioning by W.F. Stoecker

    Ken
    Thanks Ken! u've made my day.