    R407c Pressures



    Basically all I need to know are the pressures you would most likely see from a 407c split system. I need to get a base line for the pressures in both heating and cooling. Has anyone got any ideas?



  2. #2
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: R407c Pressures

    Somewhat higher than R22....

    http://www.3dair.co.uk/download-files/r407c-guide.pdf

    Good detail treatment and deals with splits in particular. See particularly lubricants.

  3. #3
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: R407c Pressures

    hi xeomus,
    R-407c on my comparitor dew 0c= 52 psig
    bubble 0c = 68 psig
    hope this helps? sedgy,

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: R407c Pressures

    Why don't you look at your comparitor and see what temperatures you want, then look at the pressure for that temperature.

    This system works for all refrigerants.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: R407c Pressures

    Quote Originally Posted by frank View Post
    Why don't you look at your comparitor and see what temperatures you want, then look at the pressure for that temperature.

    This system works for all refrigerants.
    Gee, that's too easy Frank, takes brain power that does.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: R407c Pressures

    Sometimes Brian, it's the obvious that some people can't see..

  7. #7
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: R407c Pressures

    frank and brian,
    I dont know if you are aware but a lot of youngsters < mostly in europe< dont even know what a conparitor is, never mined how to use one, as allways I was instigating the progress of the same when < as usual someone came on as usual taking the p< water out of the youngsters who want to know things, they dont want people taking the piss. its a pitty a lot of experiance engineers have not got the man management skils,
    or the teaching skils to get the best out of theses youngsters, yours sedgy= ex teacher , coach , and mentor

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: R407c Pressures

    Hi Sedgy....no intention of taking the P.... out of anyone. That's not my way, and I'm sorry if it sounded that way.

    It's just that the question is always asked 'what pressures should I be looking for?'

    Our trade is all about Temperature control but for some reason, our younger engineers (or older learners) seem only to want to know about pressures. Maybe it's the way it's taught nowadays in college, I don't know?

  9. #9
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: R407c Pressures

    sorry frank, I jumped in . again

  10. #10
    Join Date
    Jul 2010
    Location
    scotland
    Age
    49
    Posts
    71
    Rep Power
    14

    Re: R407c Pressures

    I think what you are looking for is expected running pressures of a heat pump air conditioning system and not a desired temperature for setting a freezer.
    If this is so always evaporating above zero, 4 or 5 deg celcius, R407c will have a low pressure (suction ) of about 50 psi. and a high pressure ( discharge ) of about 280 psi, which is about 55 deg celcius, cooling cycle. Standing pressure ( system not running ) will depend on surrounding temperature of outdoor unit. Cant say exact without refering to gauges or comparator.
    Hope this is of use to you. If you are have gauges refer to them, if gauges dont have R407c on them you can get pop on dials to existing gauges, save buying new ones.

    Nev
    Quote Originally Posted by Xeomus_Aevis View Post
    Basically all I need to know are the pressures you would most likely see from a 407c split system. I need to get a base line for the pressures in both heating and cooling. Has anyone got any ideas?

  11. #11
    Join Date
    Nov 2009
    Location
    UK
    Age
    33
    Posts
    7
    Rep Power
    0

    Re: R407c Pressures

    Cheers for the help guys, those of you who werent taking the micky out of me anyway. When your college / business is too cheap to provide a comparitor i sometimes forget they exist.

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: R407c Pressures

    It is not " taking the micky out of me"! You should be thankful to them, because they are not telling you pressures you expect, but guiding you in right way to do things. They are not giving you fish for one meal, they are guiding you to search for way to learn how to catch fish every time you need a meal..

    If you know basics of operation of split type air conditioner then you will know what would be temperature difference between mediums in question in both heat exchangers. These temperature differences (TD) are what is all about.
    Pressure of refrigerant depend on saturation evaporation/condensation temperature which is dependent on TD of evaporator/condenser. TD of heat exchanger is dependent on heat exchanger materials, construction, cleanliness and flow of media at exchanger.
    Some guiding numbers are:

    http://www.refrigeration-engineer.co...2775#post92775

    When you know these numbers than you know expected saturation temperatures of evaporation/condensation for your concrete case.

    When you know expected temperatures, than you know corresponding refrigerant pressures and what to look for on PT comparator or directly on gauge.

    You cannot ask for pressures without providing data about conditions. They could wary widely depending on conditions.

    Example:


    Therefore, knowing of basics of construction of split type air-conditioner will give you universal answer for all refrigerants and you will newer ask again what pressure should you expect. You will be asking what TD should be, and rest is only matter of measuring air/water temperature and according to that determining saturation temperatures and then finding corresponding pressures.

    http://www.refrigeration-engineer.co...ight=pressures

Similar Threads

  1. low pressures
    By sean1 in forum Fundamentals
    Replies: 13
    Last Post: 04-02-2010, 02:08 AM
  2. Oil pressures
    By HeathT in forum Trouble Shooting
    Replies: 2
    Last Post: 24-02-2009, 09:32 PM
  3. R22 OPerating Pressures
    By Futsal1st in forum Trouble Shooting
    Replies: 13
    Last Post: 14-02-2009, 08:52 PM
  4. Oil pressures
    By N.Lewis in forum Trouble Shooting
    Replies: 4
    Last Post: 12-02-2008, 04:23 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •