    Isceon MO29



    Has any one had much to do with isceon mo29.
    If so what are your opinions?



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Isceon MO29

    I did a refit on a Carrier water chiller original charge of R22 was 350kg ended up charging with 700kg of mo29 also we were told by dupont that the original sunsio 3gs (mineral) oil would be fine but turned out it wasn't and had to change to emkrate 68 (ester) we did loose some capacity from the system but i would use it again as the chiller does not run too bad on it all in all i suppose every application is different in my case i had recip comps and remote condensers, what application are you planning on using it for?

  3. #3
    Join Date
    May 2010
    Location
    Australia
    Age
    39
    Posts
    29
    Rep Power
    0

    Re: Isceon MO29

    well i am about to retrofit a carrier 5h120 recip set chiller with an R22 Turbocor compressor (so oil wont be much of an issue) Water cooled evap condenser. I am doing to retrofits in the near future and both machines are identical so it might be a good comparison test one on r22 one on mo29. Let the results speak for themselves.

  4. #4
    Join Date
    Sep 2010
    Location
    USA
    Age
    62
    Posts
    23
    Rep Power
    0

    Re: Isceon MO29

    There are a number of case histories posted on the DuPont website.
    http://www2.dupont.com/Refrigerants/en_US/uses_apps/case_histories/byproduct.html#mo29

    http://www2.dupont.com/Refrigerants/...duct.html#mo29
    Last edited by Brian_UK; 04-03-2011 at 08:39 PM.

Similar Threads

  1. Isceon 89
    By cryotech in forum Refrigerants
    Replies: 1
    Last Post: 30-04-2010, 05:59 AM
  2. Isceon 59 freezer puzzler
    By get the gauges in forum Commercial
    Replies: 31
    Last Post: 12-02-2008, 10:25 PM
  3. Replace R22 with Isceon 29
    By birdseed in forum Refrigerants
    Replies: 3
    Last Post: 04-12-2007, 07:11 PM
  4. HT and LT R22 systems to Isceon MO29 (R422D)
    By Steve in forum Refrigerants
    Replies: 3
    Last Post: 02-10-2007, 10:03 PM
  5. isceon 49 istead of r134a
    By dp15 in forum Refrigerants
    Replies: 2
    Last Post: 05-05-2007, 06:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •