    Hi. dear members
    I need help, suggestion, documentation ... etc ...
    .... recently one local company bought two J&E Hall mono screws type HSO 2031 equipped with economizer... compressors were purchased to work in one stage system -45*C/+35*C with ammonia .... but that never happen compressors cannot work in that range....
    ... original vendor never come back and give up, then owner engage another local company to help somehow ..... after a lot of problems and examination they found those compressor are not capable to work in that range what is visible even from compressor envelope for those compressors .... please do not ask what and why happened, I do not know and that is behind us now .... a colleague, engineer from that company asked me for help and that is reason to come on RE forums ....
    ... something must be done ...... but, what to do ...????
    it is necessary to use both almost new compressors ... one for the first stage and another for second stage ... i.e.
    .... build two stage system -45*C/-5*C and -5*C/+35*C, but we are not sure what we have to do with compressors to get some economical work ... assume, we need to change Vi, maybe on both or only one, maybe something else not sure .... unfortunately we do not have any documentation .....
    ... company sent some email asking for help to J&E Hall, but unfortunately no response (what is not nice), some response/s not even like ... you cannot do that, this etc .... or you can do that in this/that way ... owner is not blame J&E Hall for this situation, but at the end completely helpless ...
    That is the main reason to come here ....
    I do hope on this powerful forum we have members capable to help ..... with suggestion, service manual with cross-section drawings, spare part list etc...
    Thanks, its your move now appreciate any help ....
    Best regards, Josip
    3,357
    Re: Help needed J&E Hall monoscrew compresors
    http://wenku.baidu.com/view/4f5d875f...9a451a489.html
    josip check this out it may help.
    -45 sst + 35 sct looks like it will be on border to me ( see in link manual).
    If you want to make 2 stage modify compression ratio wpold be definately necassary & motor on high stage compressor
    3,357
    Auckland
    74
    3,357
    37
    They make a good mooring if you own a boat.
    Aug 2007
    Adelaide Australia
    70
    562
    Hi Josip
    I think I have some info on monoscrews at home somewhere, I will have a look and if I have anything I will email to you next week.
    Sounds like Magoo doesn't like these compressors.
    Paul
    Jan 2006
    Croatia
    68
    2,263
    31
    Hi, RANGER1
    thanks for link ....but, cannot see it ... very slow ... trying to open and save that page but no way .... waiting to open document since morning
    please, look at attached diagram from another source .... -45*C/+35*C is completely out of range ...
    motor is not necessary to change because it was intended for one stage and those motors are usually little stronger, this one is 250 kW .... its a pity to use such a big motor for the first stage ...
    Best regards, Josip
    Attached Files Attached Files
    Jan 2006
    Croatia
    68
    2,263
    31
    Hi, Magoo
    I think it is more appropriate for battleship then for a small boat
    Best regards, Josip
    Nov 2009
    france
    64
    225
    hi Josip,
    check your Email, you have some documents to read
    495
    21
    hi josip ive send you some info and i will try to find some more on the compressor rebuild side
    Jan 2006
    Croatia
    68
    2,263
    31
    Hi, gentlemen
    Quote Originally Posted by cricri View Post
    hi Josip,
    Quote Originally Posted by GHAZ View Post
    Thanks, documentation received, a lot to read and check again ...
    Ghaz it will be very nice to have some more info about rebuild side i.e. Vi change ...
    Best regards, Josip
    3,357
    josip,
    Try the second post link as I just checked & all OK.
    It is an aplications manual of 60 pages
    Jan 2006
    Croatia
    68
    2,263
    31
    Hi, RANGER1
    josip,
    Thanks, got it already.... still in researching and rechecking .... I'll come back with news, hopefully good one ...
    Best regards, Josip
    Mar 2005
    638
    With my limited experience with the single screw compressor, I found them not well suited fro such long pressure ratios in a single casing. This system should have been designed as a two stage system from the start.
    It looks like a good boat anchor system from the limited information provided.
    Ken
    Aug 2007
    42
    135
    Hello,
    Yes it is possible you will need a VR of 4.9 and they will do around 400kW only. COP is a disaster at these levels. Better to make a two stage syatem as suggested. A vr of 2.6 and 3.5 would accomplish this with a much better cop and less energy input. If you get in touch with our dartford officeand ask for design department they will help you, for a price.
    The Bridge Keeper
    'Answer me these questions three, n'er the other side ye see.'
    What is your name?
    What is your favourite colour?
    What is your suction superheat?
  1. Hall of shame.
    By Temprite in forum The Trail of Tears
    Last Post: 28-02-2011, 10:14 PM
  2. J&E Hall
    By Snicks in forum Industrial Compressors
    Last Post: 09-12-2009, 09:56 AM
  3. hall v92
    By GHAZ in forum Industrial Compressors
    Last Post: 30-04-2009, 10:31 PM
  4. Hall Monoscrew
    By PaulZ in forum Industrial Compressors
    Last Post: 28-04-2009, 12:51 AM
  5. monoscrew compressor
    Last Post: 21-10-2006, 01:20 AM
Tags for this Thread