    Floating Condensation/Suction - Electronic EPR/TXV



    Hello!!

    Do you use Floating Condensation when Parallel Compressors Rack is used??? What changes are there to be done in the components of the system???

    I've read that when use of Floating Condensation the TXV should be analized to determine if Electronic one is required, and if Floating Suction the EPR should be electronic too to ensure the correct functioning of the control.

    Also I will like to discuss the benefits of using this type of control.

    Thanks!!



  2. #2
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    OK, I guess not many use the Floating Suction or Floating Condensation...

    Any one????

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    Best described as a floating accident waiting to happen, when electronics are envolved. One hick-up one broken compressor. All in the name of progress and efficiency.

  4. #4
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    Ok, 1 vote for DO NOT USE IT !!!

    Anyone else?

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    In industrial refrigeration people use floating condensing and suction pressures. Their are good tools to save energy.
    TXV has narrow range of operating condensing pressures. So it is not good for floating. EER has wider operating range of condensing pressures.
    I assume that EPR is evaporator pressure regulator. I'm doubt that any EPR can be helpful to save energy. It is better if you do not have EPR. To save energy, compressor operating suction pressure should be floated.

  6. #6
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    Thanks Segei. One question: If you don't have EPR how do you manage diferent rooms with diferent suction pressures???

  7. #7
    Join Date
    Dec 2010
    Location
    Almeria
    Age
    50
    Posts
    6
    Rep Power
    0

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    I used floating condensation and suction.

    for example: 404a work the 15 to 20 bar (+25 to +35ºC) Dt 10ºC cop increase 20-30%.

    One degree Celsius is a 3% energy savings

    0 problems. This installation works with plc.

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    PLC's are as good as the programer, functional descriptions from the designer is only half way there. Programers always take short cuts, beleive ME. been there done that with computer nerds.
    What is the saying..., rubbish in , rubbish out. I am being polite very unusual for me. [ common comment/ didnt think that would happen or even matter. ] and you have compressor bits scattered on the floor.

  9. #9
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    Quote Originally Posted by georgedvf View Post
    Thanks Segei. One question: If you don't have EPR how do you manage diferent rooms with diferent suction pressures???
    It depends of the system. In industrial refrigeration we have 2 -3 different separate suction pressures. Each pressure has compressors operate for this particular suction. If you compressors only for low suction pressure, you should have EPR. However, it doesn't matter for efficiency it is mechanical or electronic EPR.

  10. #10
    Join Date
    Dec 2010
    Location
    Almeria
    Age
    50
    Posts
    6
    Rep Power
    0

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    Quote Originally Posted by Magoo View Post
    PLC's are as good as the programer, functional descriptions from the designer is only half way there. Programers always take short cuts, beleive ME. been there done that with computer nerds.
    What is the saying..., rubbish in , rubbish out. I am being polite very unusual for me. [ common comment/ didnt think that would happen or even matter. ] and you have compressor bits scattered on the floor.
    I am a programmer and refrigeration technician. This is the key for me if you use plc. The first is the safety of equipment.

  11. #11
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    When usign floating condensation pressure, what are the parameters to determine de best condensation pressure??? in other words, where to put sensor, transducers, etc???? what's the logic to determine the best pressure at the time???

  12. #12
    Join Date
    Dec 2010
    Location
    Almeria
    Age
    50
    Posts
    6
    Rep Power
    0

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    Pressure = Pressure equivalent to temperature (Room temperature + DT)

    IF Pressure < P min Then Pressure = P min

    Minimum pressure P min is determined by experience, type of compressors, etc.

  13. #13
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Floating Condensation/Suction - Electronic EPR/TXV

    About optimum condensing pressure.
    First you should choose the base line. For air condensers base line is dry bulb temp. For evaporative condensers base line is wet bulb temp. Than you should determine optimum approach. Approach is temperature difference between condensing temperature and base line temp. Criteria of optimum approach is minimum compressor+ condenser energy use. I've done my tests and for evaporative condensers optimum approach can vary from 8 degF to 30 degF. I think it will easier to determine optimum approach for air condensers.

Similar Threads

  1. Condensation Issues
    By Husky250 in forum Air Conditioning
    Replies: 9
    Last Post: 26-12-2010, 07:00 PM
  2. seq. suction pressure/compressor suction
    By stanthonycold in forum Trouble Shooting
    Replies: 0
    Last Post: 29-07-2010, 10:09 PM
  3. Condensation
    By syaful in forum Domestic
    Replies: 3
    Last Post: 05-03-2009, 11:48 AM
  4. pressure of floating condensation
    By german in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 25-06-2008, 12:51 AM
  5. Condensation
    By jay in forum Refrigeration Books
    Replies: 42
    Last Post: 08-11-2007, 02:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •