    Recovery Cylinder



    hi guys, came across a refrigerant reclaim cylinder with no fill values the other day only WC and TW, i couldnt find any filling factors in SI for different refrigerants so i had to use wc x 0.8 for my safe fill,

    don't suppose anyone's got a table with filling factors on have they? for common refrigerants

    if so the correct equation can be used, often you can safely fill more than the above equations answer.

    Filling Factor X tank WC ( water capacity) x 0.8 for safe fill

    Thanks guys
    Last edited by SkyWalker; 24-02-2011 at 07:21 PM.



  2. #2
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: Recovery Cylinder

    Quote Originally Posted by SkyWalker View Post

    Filling Factor X tank WC ( water capacity) x 0.8 for safe fill

    Thanks guys
    That a safe enough method just make sure the cylinder is in decent condition and the test date does not exceed 5 years

  3. #3
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Recovery Cylinder

    hi Quality, i was hoping for the "filling factor" of different refrigerants as i dont know them, not sure if you miss read?

    i want to use that equation as i said but without filling factor i cant?

  4. #4
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: Recovery Cylinder

    Yes sorry I did not read fully ,I am sure I have a chart for refrigerant factors as you called it I will look tomorrow and post

  5. #5
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Recovery Cylinder

    hi quality, dont suppose you found that table did you?

  6. #6
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: Recovery Cylinder

    I did not find but have looked high and low. If you have a safety data sheet for a particular refrigerant it should tell you the density of it which you could use for a calculation

  7. #7
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Recovery Cylinder

    Hi SkyWalker
    I need to get my Arktic license soon and would appreciate if any one could please post a link or list of the common refrigerants for filling factor or specific densities, it would be really good to find a PT chart with filling factor or densities on it. Than I could put it into my Iphone for use in the field. I do have the data for the old refrigerants but that's no good now days.
    Thanks in advance Tesla

  8. #8
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Recovery Cylinder

    hi tesla, did some research and found the following (as quality sugested) from BOC refrigerant safety sheets, will come in handy to me and hope others : -

    Relative density, liquid 1.09 (water=1) R410a

    Relative density, liquid 1.2 (water=1) R407c

    Relative density, liquid 1.2 (water=1) R22

    Relative density, liquid 1.07 (water=1) R404a

    Relative density, liquid 1.2 (water=1) R134a

    example, a cyclinder with a water capacity of 100 and you want to fill it with r407c safely

    water capacity x refrigerant density x 0.8 = safe fill

    so....

    100 x 1.2 x 08 = 96kg safe fill amount, if we dont use the density in our equation then we are using more bottles than we need to....

    100 x 0.8 = 80kg. in this example the difference is 16kg, so i think its really worth knowing refrigerant density and doing the sum.

    Hope this helps =)
    Last edited by SkyWalker; 02-03-2011 at 05:44 PM.

  9. #9
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Recovery Cylinder

    Thanks SkyWalker
    Just what I needed
    Tesla

  10. #10
    mickel's Avatar
    mickel Guest

    Re: Recovery Cylinder

    How do you determine the safe liquid level in your recovery cylinders? I have been talking to techs over the years and I always get different answers. I know the correct way is to calculate with a bunch of formulas from water cap. and ratios of saturated temps of liquid. I am talking real world. For example.. If you are using a 125# cylinder, I have been told to fill to net weight from 100# or 125#.

  11. #11
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Recovery Cylinder

    Quote Originally Posted by mickel View Post
    How do you determine the safe liquid level in your recovery cylinders?
    dude have you read this thread? the answer is staring you in the face?

    its not "a bunch of formula" its ... water capacity x refrigerant density x 0.8 = safe fill

    you get the water capacity off the bottle your filling (stamped on), and you need the liquid density of the refrigerant you intend to fill the bottle with and then you can apply the above equation in "the real world"

Similar Threads

  1. water in recovery cylinder
    By MIST HVAC RA in forum Trouble Shooting
    Replies: 14
    Last Post: 19-03-2011, 09:44 PM
  2. Is Air Content Analyzer Required on Recovery Cylinder?
    By A1_Autos in forum Air Conditioning
    Replies: 9
    Last Post: 26-03-2010, 07:48 PM
  3. cylinder adapter
    By al in forum Commercial
    Replies: 9
    Last Post: 10-02-2008, 10:48 PM
  4. vacuum in a recovery cylinder?
    By flyboy3b in forum New to RE
    Replies: 6
    Last Post: 24-09-2007, 09:38 PM
  5. Old Cylinder Disposal
    By Derek in forum Refrigerants
    Replies: 6
    Last Post: 09-02-2005, 09:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •