    Plate Heat exchanger as a economiser on NH3 systems



    Do any one have experience using brazed plate heat exchanger as a economizer on a NH3 system?

    Thanks.



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: Plate Heat exchanger as a economiser on NH3 systems

    Hi, Rajkumar

    Quote Originally Posted by Rajkumar View Post
    Do any one have experience using brazed plate heat exchanger as a economizer on a NH3 system?

    Thanks.
    Welded type like http://www.vahterus.com/en/front-page

    is working fine, proofed ..... why to take a chance with brazed one .... lower price.... maybe, but what about safety?

    Best regards, Josip
    Last edited by Josip; 24-02-2011 at 07:21 PM. Reason: add link

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Apr 2008
    Location
    canada
    Age
    75
    Posts
    94
    Rep Power
    17

    Re: Plate Heat exchanger as a economiser on NH3 systems

    Quote Originally Posted by Rajkumar View Post
    Do any one have experience using brazed plate heat exchanger as a economizer on a NH3 system?

    Thanks.
    B”H
    Rajkumar,
    Be aware that majority of PHE are brazed with big cooper % content in brazing material.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: Plate Heat exchanger as a economiser on NH3 systems

    It all depends on what ammonia comes in contact with.
    Supplier should be able to advise on this area of compatability.

    Otherwise PHE is OK to use for economizer if controlled correctly.
    Best to have modulating level control valve on the subcooled liquid you produce from it , so its a more constant load on compressor economizer port.

  5. #5
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17

    Re: Plate Heat exchanger as a economiser on NH3 systems

    Ranzer, I think you got my point. I am having trouble with Dx type Brazed Economiser (Alfa Laval Alfa Nova) System. Compressor is working at (-)42 deg C. I have Bit low load approx (60%) but i am driving the compressor at full load using the VFD. I am not getting the proper return on compressor economiser port. The Economiser liquid feed assembly is having a TX Valve.

    Do any one know what i should do to get the constant load.

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: Plate Heat exchanger as a economiser on NH3 systems

    Hi, gentlemen

    Quote Originally Posted by RANGER1 View Post
    It all depends on what ammonia comes in contact with.
    Supplier should be able to advise on this area of compatability.

    Otherwise PHE is OK to use for economizer if controlled correctly.
    Best to have modulating level control valve on the subcooled liquid you produce from it , so its a more constant load on compressor economizer port.
    It is OK to use some brazed PHE because there are some brazing material resisting to ammonia.... maybe this one too, why not .... somebody gave info to Alfa Laval about refrigerants with order ...

    Quote Originally Posted by Rajkumar View Post
    Ranzer, I think you got my point. I am having trouble with Dx type Brazed Economiser (Alfa Laval Alfa Nova) System. Compressor is working at (-)42 deg C. I have Bit low load approx (60%) but i am driving the compressor at full load using the VFD. I am not getting the proper return on compressor economiser port. The Economiser liquid feed assembly is having a TX Valve.

    Do any one know what i should do to get the constant load.
    Not sure, but seems your TX is giving too high suction superheat and there is not enough capacity... for ammonia SS can be low, sometimes, as 0K using PHE....

    But I think that TX is not the good one (maybe I'm wrong) there must be a special type of injection valve electronically operated via electronic temperature probes mounted on suction pipe running to compressor's ECO port I think that's the same as per RANGER1 suggestion ... many years ago in Turkey, York Italy installed the similar system on PHE without surge drum, similar to your economizer ... working very nice ..

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Plate Heat exchanger as a economiser on NH3 systems

    Quote Originally Posted by Rajkumar View Post
    Ranzer, I think you got my point. I am having trouble with Dx type Brazed Economiser (Alfa Laval Alfa Nova) System. Compressor is working at (-)42 deg C. I have Bit low load approx (60%) but i am driving the compressor at full load using the VFD. I am not getting the proper return on compressor economiser port. The Economiser liquid feed assembly is having a TX Valve.

    Do any one know what i should do to get the constant load.
    It is not clear for me. Why do you run compressor at 100% when load is 60%? What do you mean by not getting proper return on compressor economizer port?

  8. #8
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Plate Heat exchanger as a economiser on NH3 systems

    To be sure, we need to know all details of the compressor and economizer. I've used the Alfa Nova without any problems but a flash economizer or even a flooded arrangement of the Alfa Nova would be better.
    Anyway, DX can work. Is the expansion valve sized correctly. Is it mechanical or electronic? Is the liquid distribution tube in place inside the PHE inlet connection? Have you drained oil from the bottom of the evaporator circuit inlet connection?

  9. #9
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17

    Re: Plate Heat exchanger as a economiser on NH3 systems

    We are using the mechanical expansion valve. Earlier there was no distribution tube, now we had place the distribution tube with dia 4mm hole on each chaanel but still facing the same problem.

  10. #10
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: Plate Heat exchanger as a economiser on NH3 systems

    To me you need a very constant load for TX valve to settle down with reasonable superheat.

    As I suggested the liquid line which is the heat load for the PHE ideally should be as constant
    flow as possible .
    This is best achieved with a modulating on the vessel or whatever you are delivering high pressure subcooled liquid too.
    An EEV may be able to control more accurately with a quicker response time.

    Ley s know more about your plant & how it works.

  11. #11
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Plate Heat exchanger as a economiser on NH3 systems

    Ranger1 has a good point. If the liquid flow to the low side is through a float and solenoid valve arrangement, the DX economizer will never work. liquid flow must be almost constant for this to work.

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Plate Heat exchanger as a economiser on NH3 systems

    I am not a fan of economizers with welded type with TXV. I have killed a few on ***** plants. The thermal expansion and contraction effects over a period of time creates stress fractures and leaks, if crack occurr internally you end up sending HP liquid the econo port of screw, so then went to double plate welded PHE.
    Generally prefer flooded with surge drum header and add evap press reg and flow stop check valve on suction.
    For ammonia I prefer the stacked / re-stackable type with surge header, level controller float and pulse fill valve. The ultimate would be a closed flash shell and coil economizer.

Similar Threads

  1. Plate heat exchanger temperatures?
    By Drew in forum Trouble Shooting
    Replies: 24
    Last Post: 20-01-2010, 08:17 PM
  2. Brazed plate heat exchanger
    By nh3simman in forum Fundamentals
    Replies: 4
    Last Post: 25-10-2008, 03:37 PM
  3. Fouled plate heat exchanger
    By petrock in forum Industrial
    Replies: 16
    Last Post: 12-07-2008, 10:11 AM
  4. Replies: 15
    Last Post: 07-06-2008, 12:40 AM
  5. plate exchanger in heat recovery ventilator
    By Lc_shi in forum New Technologies
    Replies: 1
    Last Post: 17-07-2007, 04:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •