    Low oil pressure on vilter compressor



    Hey I bought a reconditioned vilter recip and it keeps cutting off on low oil pressure. During the freeze cycle the oil pressure is around 50psi but during the defrost/harvest cycle the oil pressure drops to around 5psi...help please



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: Low oil pressure on vilter compressor

    Hi bsballdreamer
    Could you give us a little more info like model#, what type (components) for oil seperation and return. And what does the comp sight glass look like at 5psi? What stage of loading also. Is there only one compressor and what is it cooling. Super heat would be good too. And any thing else you think might be helpful.

  3. #3
    bsballdreamer's Avatar
    bsballdreamer Guest

    Re: Low oil pressure on vilter compressor

    It is a vilter 456xL. I use it to run a volt ice maker with ammonia. It was low on oil but that poses a different problem...where is my oil going? There is a small amount of oil dripping near my high side shut off valve?

  4. #4
    bsballdreamer's Avatar
    bsballdreamer Guest

    Re: Low oil pressure on vilter compressor

    Got it all straight thanks.

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Low oil pressure on vilter compressor

    during defrost time might you liquid returning to compressor . what is your suction pressure in defrosting time .
    oil cycling in system so you should have enough oil in compressor and all filters should be clean
    tight all nuts at shut off valve

Similar Threads

  1. vilter screw vs vilter reciprocating
    By lynark in forum Technical Speculations
    Replies: 1
    Last Post: 20-10-2010, 10:00 AM
  2. vilter compressor
    By lynark in forum Trouble Shooting
    Replies: 9
    Last Post: 22-08-2010, 02:11 AM
  3. Vilter compressor unloader valve
    By duke717 in forum NH3
    Replies: 11
    Last Post: 17-08-2010, 03:06 AM
  4. Vilter HP compressor
    By coolcmt in forum Industrial Compressors
    Replies: 1
    Last Post: 26-06-2010, 08:47 PM
  5. Compressor with no pressure difference
    By marc5180 in forum Air Conditioning
    Replies: 21
    Last Post: 17-12-2009, 09:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •