    So how does a provision refrigeration plant work? With 3 "FRIDGES"



    I am trying to make a schematic of a provision refrigeration system. Which is running 2 compressors and has 3 fridges. It has to be a simple drawing, with no refrigerant types, hi - low pressure cutouts etc..

    Until now I have made a schematic like this:


    projec.jpg
    But it looks like it will not work this way, as we know the temperature depents on pressures. In my schematic the pressures in every fridge are the same = same temperatures in each fridge.

    or there is a possibility to fit different size TX valves into each line to achieve different temperatures?

    Thanks guys



  2. #2
    Join Date
    Feb 2011
    Location
    EU
    Posts
    7
    Rep Power
    0

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Can anyone please also comment what have to be the evaporation temperatures of the refrigerant in each evaporator to reach temperatures as stated? -20C, +2C and +10C. If we use for example R404 refrigerant.

  3. #3
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    evaporation temp is 5 degrees lower than setpoint regardless of refrigerant type under normal circumstances you could use evaporator pressure regulators (EPR) to control your temp rather than expansion valves, you provide constant liquid refrigerant to the EPR which you pre set to your desired temp

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    A sample diagram is here with all of the parts...

    http://www.sporlanonline.com/5-180_072010.pdf

    Also for documentation on the various components see here also...

    http://www.sporlanonline.com/literature.shtml
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2011
    Location
    EU
    Posts
    7
    Rep Power
    0

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Thanks guys, my system has to be with a TXV, rather than with EPR.

    From which aspect does the boiling point depend on, and what does it mean "R-134 boling point -26,2C"

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    water boils and begins to have a latent heat change at 100c water-steam
    R134a does the same exept liquid to vapour at -26.6c

  7. #7
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Use the EPR's with TXV's
    -http://www.sporlanonline.com/90-20.htm

  8. #8
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    First you need to add more valves

    mark 1 on the drawing: you need evaporating pressure regulators on the suction of the two cold (3*C) and cool (10*C) rooms, because they have a higher evaporating pressure than the freezing room.
    http://www.danfoss.com/Products/Cate...e502a4f50.html

    mark 2 on the drawing: You need a non return valve on the suction of the freezing room, this to prevent refrigerant from migrating to the freezing room evaporator when the temperature controller to that room closes the solenoid valve.

    using R-404a as a refrigerant

    (ms paint edit )


    Bonus points: if the freezing and cool room has reached it's temperature and the solenoids are closed, but the compressor is to big to run the cold room alone and keeps pumping down. You can rig the wiring so that the freezing room solenoid is activated (as long as it is not in a defrost cycle), this should give the compressor enough capacity to keep running and be able to maintain the temp in the cold room.
    -Cheers-

    Tycho

  9. #9
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Can't you have one condenser with NRV in compressor discharge lines.

    More bonus points for noting capacity of rooms. The lowest temp room should be about 60% of the load on the system. This way the 2 other rooms reach temp and close LLSV then the suction pressure drops and the low temp room starts to pass refrigerant through the NRV as Tycho suggests. That's the theory I've read for 2 different rooms on 1 system so I think it would follow for 3.
    Take a butchers at the Danfoss website. I think it's mentioned in Fitters Notes.

    Cheers,

    Andy.
    Health and safety first..........unless I'm in a hurry.

  10. #10
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Quote Originally Posted by Tayters View Post
    Can't you have one condenser with NRV in compressor discharge lines.

    More bonus points for noting capacity of rooms. The lowest temp room should be about 60% of the load on the system. This way the 2 other rooms reach temp and close LLSV then the suction pressure drops and the low temp room starts to pass refrigerant through the NRV as Tycho suggests. That's the theory I've read for 2 different rooms on 1 system so I think it would follow for 3.
    Take a butchers at the Danfoss website. I think it's mentioned in Fitters Notes.

    Cheers,

    Andy.
    You could do with 1 condenser as you said, but if it is for a provision plant on a ship that spends a long time at sea, they will have a "standby" compressor unit.

    On supply ships for the oil industry they also charge both compressor units with enough ***** to run the system, so if a condenser starts leaking, they can seal that one out of the system and start the other one with no downtime.

    On fishing vessels they have two units, but only enough ***** to run one at a time.
    -Cheers-

    Tycho

  11. #11
    Join Date
    Jul 2011
    Location
    Malaysia
    Posts
    7
    Rep Power
    0

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Do anyone know how to properly to do compressor sizing? 3 rooms have different evaporating temp. Condensing temp is around 40 degC. Let say +10 room required cooling is 10000 btu/h, +2 room at 12000 btu/h and -20 room at 15000 btu/h.

  12. #12
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Off topic - needed removing
    Last edited by chillerman2006; 08-09-2011 at 03:51 PM.
    If the World did not Suck, We would all fall off !

  13. #13
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Quote Originally Posted by james10 View Post
    evaporation temp is 5 degrees lower than setpoint regardless of refrigerant type under normal circumstances you could use evaporator pressure regulators (EPR) to control your temp rather than expansion valves, you provide constant liquid refrigerant to the EPR which you pre set to your desired temp
    Quote Originally Posted by SchoolBoy View Post
    Thanks guys, my system has to be with a TXV, rather than with EPR.

    From which aspect does the boiling point depend on, and what does it mean "R-134 boling point -26,2C"


    Reading this thread is like the blind leading the blind.
    Last edited by 750 Valve; 10-09-2011 at 08:58 AM.
    ...and she said "give it to me you big fridgie"

  14. #14
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Hey 750, How's it going?
    I've been away for a month or two sorting out the calibre I need for the future hole in my head.
    What have you been up to?
    tycho was right wasn't he?

    edit: duh EPRs needed of course on the med temps, nothing needed for the freezer (except a CPR)
    beep boop bop, I am a robot that reads fault codes, voltages, amps, diodes, thermistors etc in sh1tty domestic a/c - refrig
    Last edited by paul_h; 11-09-2011 at 05:43 PM.

  15. #15
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Evening Paul

    or I should say Morning,

    I normally find systems with multi evaps, require 'EPR's on the chilled sections to prevent them freezing the produce & 'LLS' on every circuit to shut them down on their stat's ...

    R's chillerman
    If the World did not Suck, We would all fall off !

  16. #16
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    What's a chiller?
    Pretty sure I worked on one in 1993.
    Yeah I figured the EPR out myself.
    Sorry, normally late at night when I post here

  17. #17
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: So how does a provision refrigeration plant work? With 3 "FRIDGES"

    Quote Originally Posted by paul_h View Post
    I am a robot that reads fault codes, voltages, amps, diodes, thermistors etc in sh1tty domestic a/c - refrig
    Yeah ok

    Have seen alot of your posts, lots of common sense, educating us older folk,

    R's chillerman
    If the World did not Suck, We would all fall off !

Similar Threads

  1. What is the best "reasonably" priced book for Learning Refrigeration?
    By TheFridgeMan in forum Refrigeration Books
    Replies: 2
    Last Post: 21-06-2010, 12:11 PM
  2. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 06:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •