USing EES to calculate the dryness of the refrigeratant R600a flowing in a capillary
moring to all!
I've recently used EES to simulate the flowing of R600a in a capillary.And I find that using the correlation: A=0.719*B^0.403*C^-0.590*D^0.157 can causing a quite big diviation up to 35% from the experimental data. However the correlation is conclude from the experimental data and the author declared that the bias was within 10%. So I want to know if anyone have similar experience? The article is <An experimental analysis of adiabatic capillary tubes>. The after is my EES code:
module getm_ch(L_cap,D_cap,P_in,DELTAT_sc,m_h)
T_f=temperature(Isobutane,p=p_in,x=0)
T_sc=T_f-DELTAT_sc
mu_f=viscosity(Isobutane,P=P_in,T=T_sc)
v_f=volume(Isobutane,P=P_in,T=T_sc)
c_pf=specheat(Isobutane,P=P_in,T=T_sc)
A=m/(D_cap*mu_f)
B=D_cap^2*p_in/(v_f*mu_f^2)
C=L_cap/D_cap
D=D_cap^2*c_pf*DELTAT_sc/(v_f^2*mu_f^2)
A=0.719*B^0.403*C^(-0.590)*D^0.157
m_h=m*convert(kg/s,kg/h)
"结果输出"
END
call getm_ch(2.926,0.00077,721000,4.2,m)
call getm_ch(2.926,0.00077,923000,3.7,m1)
call getm_ch(2.926,0.00077,1119000,15.7,m2)
-
18-02-2011, 02:00 PM #2
Re: USing EES to calculate the dryness of the refrigeratant R600a flowing in a capill
To addition, the correlation and code are all to calculate the choked mass flow-rate in the capillary under certain conditions.
Similar Threads
-
From R600a to R12
By mlfather in forum RefrigerantsReplies: 2Last Post: 03-08-2009, 03:55 PM -
Too much noise due to air flowing
By elpajaroloko in forum Air ConditioningReplies: 4Last Post: 27-05-2009, 09:32 AM -
R600a
By Minestrone Dave in forum RefrigerantsReplies: 4Last Post: 02-10-2007, 10:33 AM -
R600a
By fireblade in forum RefrigerantsReplies: 12Last Post: 23-07-2006, 10:57 PM