    Natural (gravity) air soil venting on cold stores (-25ºc)



    Guys I'd like to get some drawings about the heating soil to prevent freezing by natural air convection. I have 1 of them but I don't agree with the air sense indicated on it...I think that the inlet of air should be at the higher air tube (2,5 m) and the lower tube (0,5 m) should be the outlet (considering that both are at the same exterior temperature).

    Awaiting your news

    Regards


    To make progress is never good enough, I want to do better and better and better

  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    Quote Originally Posted by Sandro Baptista View Post
    Guys I'd like to get some drawings about the heating soil to prevent freezing by natural air convection. I have 1 of them but I don't agree with the air sense indicated on it...I think that the inlet of air should be at the higher air tube (2,5 m) and the lower tube (0,5 m) should be the outlet (considering that both are at the same exterior temperature).

    Awaiting your news

    Regards

    Sorry the insistence
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,120
    Rep Power
    25

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    Hey Sandro
    I'm not too sure if this is the ASV your referring to but have a look at these.
    http://www.google.ie/images?hl=en&rl...w=1066&bih=590
    All the best
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    Quote Originally Posted by stufus View Post
    Hey Sandro
    I'm not too sure if this is the ASV your referring to but have a look at these.
    http://www.google.ie/images?hl=en&rl...w=1066&bih=590
    All the best
    Cheers
    Stu
    Thanks stufus, I have to say I get lost with so different pictures. I couldn't find what I looking for:

    » I'd like to get a diagram with venting pipes or "concrete ducts" underneath the floor insulation of a cold store negative temperature so to prevent the freezing of soil by natural air convection. As you should know a main inlet tube is used and a main outlet tube is used. The several pipes that run inside the cold store are connected in parallel to those main tubes.
    One of the main tube is elevated (+2,0m as example) and the other is at (+0,5m as example). Supposing that both the main tube are subjects to the same exterior temperature (higher than the cold store soil temperature) and pressure I think the air should out by the lower main tube and enters by the higher tube. However I've see an diagram where the air sense is reversed.

    What's your opinion? Do you have any any diagram that testify what I mentioned?
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    I've seen it twice with very, very bad results (condense building up in the tubes and finally resulting in a good isolator)
    Pictures already posted in the past here on RE.
    They installed a tube that went even higher than the roof so that a natural convection took place.
    Air under the soil should be colder then ambient.
    How the flow will be? Difficult to predict: will depend on conditions outside/conditions soil, wind direction and speed around the building creating a negative or a positive pressure.
    I should never do this again, radiant heating is safer, cheaper and better, in fact perfect controllable.
    If you want to install an air net, Install tubes and connect it all to a fan so that air can be forced through it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    Hi, Sandro

    Quote Originally Posted by Sandro Baptista View Post
    Guys I'd like to get some drawings about the heating soil to prevent freezing by natural air convection. I have 1 of them but I don't agree with the air sense indicated on it...I think that the inlet of air should be at the higher air tube (2,5 m) and the lower tube (0,5 m) should be the outlet (considering that both are at the same exterior temperature).

    Awaiting your news

    Regards


    Attached you can see similar installation for one cold store installed in the year 2004.... simple, but so far I do not know if they faced some problems later on ... I assume not ...

    Cold air is more dry thus heavier and by gravity going out within sloped tube causing "under pressure" at intake so the fresh air is coming in ... natural flow ...


    P_01 Model (1).pdf


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    Quote Originally Posted by Josip View Post
    Hi, Sandro





    Attached you can see similar installation for one cold store installed in the year 2004.... simple, but so far I do not know if they faced some problems later on ... I assume not ...

    Cold air is more dry thus heavier and by gravity going out within sloped tube causing "under pressure" at intake so the fresh air is coming in ... natural flow ...


    P_01 Model (1).pdf

    Best regards, Josip
    So, for the same outside conditions the air would enter at the higher tube and outs at the lower tube, right?
    The slope have the main purpose of draining water from the moisture condensation. If no slope exists it would have exist natural convection at the same.

    Thanks a lot Josip
    To make progress is never good enough, I want to do better and better and better

  8. #8
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,120
    Rep Power
    25

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    Quote Originally Posted by Sandro Baptista View Post
    Thanks stufus, I have to say I get lost with so different pictures. I couldn't find what I looking for:

    » I'd like to get a diagram with venting pipes or "concrete ducts" underneath the floor insulation of a cold store negative temperature so to prevent the freezing of soil by natural air convection. As you should know a main inlet tube is used and a main outlet tube is used. The several pipes that run inside the cold store are connected in parallel to those main tubes.
    One of the main tube is elevated (+2,0m as example) and the other is at (+0,5m as example). Supposing that both the main tube are subjects to the same exterior temperature (higher than the cold store soil temperature) and pressure I think the air should out by the lower main tube and enters by the higher tube. However I've see an diagram where the air sense is reversed.

    What's your opinion? Do you have any any diagram that testify what I mentioned?
    To be honest Sandro my opinion wouldn't be worth much as what i know about ASV could be written on the back of a postage stamp.
    I have discussed with others and made the decision it's not for me ,I'm not aware of it ever having been implemented in cold store applications in Ireland.(I could be wrong)
    So I'll stick to what i know (which isn't much)
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  9. #9
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    [IMG]file:///C:/TEMP/moz-screenshot.png[/IMG]doc1.jpg

    Hi guys,

    Continuing this "boring" subject do you think this is right? That's all this about to get a schematic with opposite sense of the air.

    I could go to see one natural circulating system to prove it if I knew some.
    To make progress is never good enough, I want to do better and better and better

  10. #10
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    Please send me your ideas/comments.
    To make progress is never good enough, I want to do better and better and better

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    I don't see why you want it to do this way if a radiant heating is
    cheaper,
    safer,
    works better,
    better controllable,
    installs faster,
    ...
    Why taking risks with something which can never be adjusted, adapted nor repaired in the future? If this fails, then you have to demolish the whole freezer !
    Last edited by Peter_1; 27-02-2011 at 09:50 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    The Client wants like that way with air...
    To make progress is never good enough, I want to do better and better and better

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    Ok, his choice then.But I may hope you advised and warned him correctly.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Natural (gravity) air soil venting on cold stores (-25ºc)

    About the sense of the air on the doc1.jpg I have sent previous do you have any comment?
    To make progress is never good enough, I want to do better and better and better

Similar Threads

  1. Typical air changes in the cold stores
    By smpsmp45 in forum NH3
    Replies: 5
    Last Post: 25-07-2010, 10:50 AM
  2. Fresh air in the Cold stores
    By smpsmp45 in forum NH3
    Replies: 15
    Last Post: 09-05-2009, 01:20 AM
  3. Doorless Cold Stores
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 08-06-2007, 10:47 AM
  4. lighting in cold stores
    By smpsmp45 in forum Electrical
    Replies: 0
    Last Post: 29-05-2007, 01:57 PM
  5. Meat cold stores
    By dogma in forum Refrigeration Books
    Replies: 1
    Last Post: 18-04-2006, 01:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •