Results 1 to 32 of 32
    Jul 2005
    Malaysia
    44
    66
    Cold storage - Onions room
    Dear all,
    To size a chiller room (0 to -3 deg C) for onion and garlic room. Any special coatings required on unit coolers cooling coil?
    Products are exposed and stacked using pallets.
    Any other things to take note, such as ventilation etc?
    Thanks a lot...
    Dec 2004
    LEBANON
    44
    854
    Re: Cold storage - Onions room
    Yes the odor of the onion and garlic , you sure need a super shower each time you enter the room
    Dec 2004
    Australia
    52
    519
    I couldnt say for sure but, I think you would definetly have to treat the evaporator.
    Underbench fridges are notorious for losing the evap coils due to the corrosive nature of the foods that are stored in them.
    Some manufactures supply treated evaporators or you can buy cans of it yourself to treat the coils.
    Chemi mentioned spraying I think epoxy resin into evaporator coils in a coolroom storing cheese I think.
    He may well be able to give you some good advice.
    Aug 2005
    5,302
    Kevin,
    Here is some additional information you may find useful,
    http://vric.ucdavis.edu/selectnewtopic.undergnd.htm
    Look under the section titled "Recommended Storage Conditions"
    http://www.extension.umn.edu/distrib...0.html#1005-26
    Here is a link to a coating supplier. I have used this before on applications where corrosion was anticipated. Since this is a coating, it can be damaged. Once this happens, it is only a matter of time until the corrosion gets under the coating.
    http://www.heresite.com/index.htm
    I don't have any first hand experience with this commodity, but hope the information above helps you.
    You might also try the ASHRAE handbooks. Otherwise, you need to find someone who has done this before.
    I would recommend the pallets be stacked on racks to promote even air circulation over the products. Also, the pallets should not be stacked too close to the walls.
    This allows the air to circulate around the pallets, and helps to maintain a uniform air temperature around the pallets.
    The unit coolers should be located away from the walls at least equal to the unit cooler height. More if possible.
    I would also suggest the air flow from the unit coolers to be directed towards the storage doors. This helps to control infiltration of moisture and helps to reduce condensation on the bottom of the unit coolers, when warm air enters.
    I would not recommend the unit coolers be placed above the storage doors. This is when condensation occurs on the unit cooler drain pans.
    Regards,
    5,668
    Don't forget to allow for the decrease in effiecency of the coil due to the coating when sizing the evaporator
    Sep 2005
    Atlanta Georgia USA
    80
    Thumbs up Re: Cold storage - Onions room
    US Iceman is right on target.
    We have done these rooms with the heresite coating, it gives good corrosion protection, minimum heat transfer reduction (less than 1%), and no bridging.
    You might also consider using copper fins.
    Steve
    Sep 2003
    ISRAEL
    72
    4,248
    Hi Steve/
    Its the first time I hear about keeping onion and garlic in cold storage.
    We keep them uot' in the sun so they will get dry.
    Chemi
    Oct 2003
    5,630
    Goedhart makes stainless steel evaporators +/- 20% to 30 % more expensive than the standard types.
    I think you have to store them the same way we store here apples and pears in a CA.
    Sep 2005
    Atlanta Georgia USA
    80
    Yea Chemi
    In the US we eat our onions wet and our garlic dry.
    Haven't you heard that the Vidalia onion is the sweetest in the world, we have people that make sandwiches out of them.
    I like to hear from you and guys like Peter_1 because I'm learning about how you guys do things in the other part of the world.
    Steve
    Dec 2004
    LEBANON
    44
    854
    I can't support onions , the only way that i eat it , is coocked , and with other things , maybe in salad (occationally) . . . but eating an onion sandwich ....................................
    Oct 2004
    Scotland
    1,454
    Onions are my farourate food have them with anything or just on there own.
    mmmmm nice.
    and go get a cuppa
    Dec 2004
    LEBANON
    44
    854
    Annnnnnd girls will like you Chillin , after some fresh onions , you will be the most wanted by women
    Aug 2005
    5,302
    Hi Botrous,
    I went to school with a girl who ate onion and peanut butter sandwiches. She was a very nice looking girl who had no shortage of guys chasing her.
    Perhaps if it was the guys eating the sandwich and chasing girls the situation might be different???
    Sometimes it does not matter, heh?
    US Iceman
    Dec 2004
    LEBANON
    44
    854
    I bet this is true
    Oct 2004
    Scotland
    1,454
    Hope not, wife might not like that.
    US Iceman
    You saying I want guys chasing me?
    and go get a cuppa
    Dec 2004
    LEBANON
    44
    854
    She sure will not
    Aug 2005
    5,302
    Hi Chillin out,
    Quote Originally Posted by Chillin out
    That is not exactly what I had in mind!!!
    US Iceman
    Vandy422's Avatar
    Vandy422 Guest
    Quote Originally Posted by Steve Wright
    Steve
    I have specked Heresite before but with poor results as it is brittle and pops off of the fins. Carrier had recommended an Epoxy Ecoat called ElectroFin which we now recommend on harsh or corrosive applications. Have not had any complaints in 3 years.
    Jul 2005
    Malaysia
    44
    66
    Guys,
    Thanks for the useful information.
    rgds,
    Kevin
    Sep 2003
    pa
    We stored WALA-WALA and Vidalia in our cold storages during the years 1992-1996.
    Ideal storage is 65% Rel. Humidiy at 34 deg.F.
    We were able to convert our apple storage buildings to make the above parameters for the onions.
    Onions came to us wet. For the first 3 days, we used the evaporator fans to dry them out. When the rooms got to be about 65% rel. hum, we then started lowering the temp.
    To keep the RH in check, it was necessary to create a load (heat gain) by turning on the defrost heaters for an hour at a time on one system while refrigerating the room with the other system.
    AIR MOVEMENT over the boxes of onions is crucial.
    Sweating of the onions will occur in July after taking them out of the cold storage. However, the refrigerated containers used for shipment kept the temp at 55 deg. F, and the RH at 65%.
    Ideal marketing is put the onons in an air conditioned food market., not in a walk-in cooler.
    Chandra's Avatar
    Chandra Guest
    I am planning to start a Cold Storage units for Onions and Tomattos. I live in India. Could you please someone kindly guide me - what are the procedure and where can i find information about how to store onions/tomato/potato, what type of cold-storage units require to store onions /tomattos/potato.
    Chandra
    Croatia
    68
    2,261
    Hi, Chandra
    welcome to RE forums...
    Quote Originally Posted by Chandra View Post
    Chandra
    Please make search on RE forums....there are a lot of posts with links to appropriate documentation regarding...harvesting...post harvesting...and storage of onion/potato/tomato
    for beginning, here is one link....
    http://www.fao.org/inpho/content/com....htm#TopOfPage
    hope that is of some help
    ....it is not a simple task at all
    Best regards, Josip
  23. #23
    Jan 2008
    India
    14
    To get the temperature of onions you must run your compressor at lower suction i.e. 12- 15 C TD. As TD is higher RH decreases. In onion cold store you require hot gas or electric heaters defrosting and heater bank at the front of cold coils i.e at the discharge of air.
    Thx.
    regards
  24. #24
    Apr 2006
    Canada
    154
    Hi Chandra,
    For Onions and garlic storages, RH plays a vital role.
    You have to use reheat system.
    Regards,
  25. #25
    May 2006
    India
    82
    1,013
    Hello Chandra,
    What exactly would you like to know about the storage facilitiy. Every product has its individual requirement. To be able to help you, I would like to know the specific product, quantities, from where is it coming ie. from the field after harvesting or are they from the market etc.
  26. #26
    May 2006
    India
    82
    1,013
    Hi jwasir,
    Onion and garlic requires a RH ranging from 70 to 85%. I do not feel that reheat is required. The evaporators should be capable of maintaining this RH. It is because of these reasons, that I always suggest that individual produces should have separate rooms as each product requires a different temperature and humidity
  27. #27
    Apr 2006
    Canada
    154
    Dear Mr. Sen,
    In one case we were having problems as garlic was getting wet but temp. was going down.
    So we have to add some resisitive heaters in the room.
    You are absolutely correct that individual produces should have separate rooms.
    Sometimes there is misconception between absolute humidity and relative humidity.
  28. #28
    Michael Kennedy's Avatar
    Michael Kennedy Guest
    Chandra
    This is my first post to Re
  29. #29
    respiration rates are high and humidity control is critical, would recommend stainless steel pipe and fin evaps and CO2 monitoring with lots of fresh air make up, as they can go to mush over night if RH and CO2 get out of spec..
    cheers Magoo
  30. #30
    Split Croatia
    6,151
    Quote Originally Posted by Michael Kennedy View Post
    I love tradesman's!
    After journalists, then politicians and lawyers, they are most agile kind of peoples. I wish I could have at least 10% of their agility.
  31. #31
    Apr 2007
    izmir
    38
    be careful about moisture otherwise onions can leaf out and turn green
  32. #32
    Apr 2006
    1,620
    Well michael keep going at that rate will end up being your last post!
  1. Cold Room Design - minus 25deg C
    By vijay_study in forum Fundamentals
    Last Post: 11-11-2009, 07:12 AM
  2. Cold Room Design
    Last Post: 09-07-2007, 08:11 AM
  3. troubleshoot a two door storage room
    By duraid in forum Fundamentals
    Last Post: 13-12-2006, 06:57 AM
  4. Cold room box required
    By Andy W in forum Commercial
    Last Post: 19-07-2006, 08:48 PM
  5. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Last Post: 12-03-2006, 09:20 PM