    J e hall unloader problem



    Hello can anyone help with a problem with a V 92 6 cyl J E HALL ammonia compressor. I have low oil pressure about 15 psi and the unloaders will not load up. I changed the oil and cleaned the oil pump intake screen, did not help. I can manually operate the unloaders by forcing oil into port on bottem of unloader with hand oil pump but they will not load up on their own. Soleniods are working.



  2. #2
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: J e hall unloader problem

    Hi Hall v92 compressor has 2 oil filters 1 inside the sump and 2nd at the back near the oil pump ,which cant be clean and has to be replaced because its like a cloth filter, and the unloading cage around the cyclinder has 2 miliflex seals which come in pairs 1 for liner and the other for the moving part of the cage,and if they are worn then the oil leaks out and the pins dont drop to lower the suction ring valve,

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: J e hall unloader problem

    Agree with GHAZ, you need oil pressure to load compressor, oil pressure is the real problem, from memory the minimum diff pressure above suction is 35psig. The loader sleave seals on piston liners can be a problem as they wear and go brittle with age.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: J e hall unloader problem

    Welcome to the forum referdan.
    Just to ad to the good advice of Ghaz and Magoo.
    Several things differ,dependant upon whether you have a Mk1 or Mk2 machine?
    If i remember correctly the Mk1 is energise to unload and the Mk2 is energise to Load I think?
    How many cylinders the comp has.
    The oil strainer on a 3 or 4 cylinder machine is inserted heater rod style below the back end cover.
    In the sump,as mentioned on a 6 or 8 cylinder machine.


    Assuming you have not serviced the said machine recently? (Do you know when it was last serviced?)
    The expected oil diff when running is between 30-50psi. The actual oil pressure shown by the gauges is not critical provided it is sufficient to close and maintain the oil diff switch in the closed position.

    Proving with a hand pump each solenoid valve assembly seem to rule out the likelyhood of damaged or worn line seals.
    Assuming you have proven each solenoid assembly.
    Oil Temp?
    The Oil Pressure Relief valve malfuntioning?
    Has someone used a different oil to the norm?
    Excessive internal wear.

    It sounds as if this machine is due some TLC.
    Good luck Grizzly.

  5. #5
    referdan's Avatar
    referdan Guest

    Re: J e hall unloader problem

    Thank you gentlemen.I found the internal oil filter it was callapsed! very dirty.I have ordered some replacements.

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: J e hall unloader problem

    Hi, referdan


    Quote Originally Posted by referdan View Post
    Hello can anyone help with a problem with a V 92 6 cyl J E HALL ammonia compressor. I have low oil pressure about 15 psi and the unloaders will not load up. I changed the oil and cleaned the oil pump intake screen, did not help. I can manually operate the unloaders by forcing oil into port on bottem of unloader with hand oil pump but they will not load up on their own. Soleniods are working.

    Quote Originally Posted by referdan View Post
    Thank you gentlemen.I found the internal oil filter it was callapsed! very dirty.I have ordered some replacements.
    I don't want to be rude, but we have to check complete oil circuit when we have low oil pressure ....

    .... oil filters the first, because they are installed to protect machines from some other bigger damage ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: J e hall unloader problem

    Thanks for the post referdan.
    I am gad you were able to sort your problem.
    May I add for us oldies it's sometimes a case of "The more you know the worse the problem is".
    Sometimes forgetting, or assuming the obvious.
    If you need any more assistance just post. There are a lot of "us" with Halls knowledge.
    And welcome to the forum.
    Grizzly

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: J e hall unloader problem

    Hi, Grizzly

    Quote Originally Posted by Grizzly View Post
    Thanks for the post referdan.
    I am gad you were able to sort your problem.
    May I add for us oldies it's sometimes a case of "The more you know the worse the problem is".
    Sometimes forgetting, or assuming the obvious.
    If you need any more assistance just post. There are a lot of "us" with Halls knowledge.
    And welcome to the forum.
    Grizzly
    Agree with you, this is not the first time when we try to help, but .... due to missing "root" info from OP we are heading our detection in wrong direction .... that's the reason to ask OP for as much as possible information ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: J e hall unloader problem

    Check your loading seals also as they cause these symptoms.
    The Bridge Keeper
    'Answer me these questions three, n'er the other side ye see.'
    What is your name?
    What is your favourite colour?
    What is your suction superheat?

  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: J e hall unloader problem

    Quote Originally Posted by HallsEngineer View Post
    Check your loading seals also as they cause these symptoms.
    You didn't bother to read the above posts then?
    Grizzly

  11. #11
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: J e hall unloader problem

    Yes i did.
    The Bridge Keeper
    'Answer me these questions three, n'er the other side ye see.'
    What is your name?
    What is your favourite colour?
    What is your suction superheat?

Similar Threads

  1. Bitzer compressor unloader
    By RINBERT CG in forum Trouble Shooting
    Replies: 1
    Last Post: 08-10-2010, 07:26 PM
  2. Stal S24 unloader and feedback
    By fireandice in forum Industrial Compressors
    Replies: 0
    Last Post: 19-07-2010, 09:42 PM
  3. Unloader
    By Abe in forum Fundamentals
    Replies: 6
    Last Post: 15-10-2009, 10:33 PM
  4. Copeland Compressor Suction Unloader
    By iceman007 in forum Commercial
    Replies: 3
    Last Post: 14-10-2009, 11:04 AM
  5. Unloader Set points
    By KeithCA in forum Trouble Shooting
    Replies: 4
    Last Post: 07-09-2005, 06:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •