    Mitsubishi electric PUH-P100



    Hi I have a outdoor unit I put on test then the outdoor unit comes on the pipes starts freezing up and the receiver as well the outdoor fan just goes really slow for a min then it cuts out, put the gauges on when running on cooling gas pressure and power is fine on the indoor ducted unit theres no air pressure coming out of vents which it did work fine the code comes up on test run high abnormal temperature can any one help.
    This unit is only 3 month old
    Last edited by eurocooling; 17-02-2011 at 07:13 AM.



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi electric PUH-P100

    If you can provide exact model of the outdoor & indoor units together with the exact fault code that would be helpfull.

    If the indoor unit does not run the fan or there is some reason why there is no air flow through the indoor coil then in cooling mode the suction will frost & the system will stop on a fault.
    Perhaps something simple like closed fire damper in the ductwork ?

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Mitsubishi electric PUH-P100

    Sorry mate, we all have to get dirty sometimes.
    Get in the ceiling.
    Is the fan running?
    If not - is there power to it, or a cap OK, or the windings normal resistance
    If the fan is running - is the return duct clear, is the outlet ducting good.

    With ducted a/c, you have to go into the ceiling, not troubleshoot from the outdoor unit, or the indoor outlets only.
    Last edited by paul_h; 17-02-2011 at 05:45 PM.

  4. #4
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Mitsubishi electric PUH-P100

    Hi indoor unit fan works fine the duct system all clean inside blows fine on fan only

  5. #5
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Mitsubishi electric PUH-P100

    Hi the code coming up on the remote after test run is U1 this says abnormal high pressure overheating safeguard operation the model is Mr slim Pead-100 hope you can help as I live in Portugal and mitsubishi are not the best help here

    Regards

    Jason

  6. #6
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi electric PUH-P100

    U1 is high pressure safety switch activation

    On R410a thats 4.15 MPa or aprox 41 bar

    Suggest look at the following items

    1/ Indoor air flow in heating mode
    2/ Outdoor fan in cooling mode
    3/ Refrigerant flow blockage ( outdoor LEV locked shut )
    4/ 4WRV not operating

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi electric PUH-P100

    service valves on the condenser closed,short of gas!

  8. #8
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Mitsubishi electric PUH-P100

    Or non-condensables.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  9. #9
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Mitsubishi electric PUH-P100

    Hi again check everything on indoor unit blowing out hot air and cooling ok,when it gets to the vents nothing coming out this was perfect 3 months ago the outdoor unit comes on but the outdoor unit fan is very slow then compressor just switches of after 5 mins

  10. #10
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Mitsubishi electric PUH-P100

    Look for dampers in the ductwork, eg manual dampers used for balancing, electric dampers used for zoning or fire dampers designed to close with fusible links if commercial property.
    Also butterfly dampers may be fitted in the outlets may have closed themselves.
    Last edited by paul_h; 26-02-2011 at 12:26 PM.

Similar Threads

  1. mitsubishi electric v mitsubishi heavy ind
    By coolhibby1875 in forum Air Conditioning
    Replies: 8
    Last Post: 04-09-2009, 01:42 PM
  2. Mitsubishi Electric P3 Error
    By tonyh in forum Air Conditioning
    Replies: 2
    Last Post: 09-08-2009, 10:47 PM
  3. Mitsubishi Electric VRF
    By vijay_study in forum Air Conditioning
    Replies: 3
    Last Post: 06-11-2008, 10:03 AM
  4. Mitsubishi Electric VRF help
    By marc5180 in forum Air Conditioning
    Replies: 10
    Last Post: 04-11-2008, 09:40 AM
  5. mitsubishi electric a/c
    By bellaman in forum Air Conditioning
    Replies: 6
    Last Post: 02-08-2008, 06:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •