    System capacity



    Hi can any one help
    If you divide the net refrigeration effect by the COP do you get the actual Kw of the system, if not is there a formula to find it, many thanks


    if you cant't fix it don't

  2. #2
    Join Date
    Dec 2008
    Location
    usa
    Age
    83
    Posts
    34
    Rep Power
    0

    Re: System capacity

    You are correct. By definition COP = Energy output divided by energy input. Thus energy input is equal to refrigeration energy putput divided by COP. Of course, all the terms in the equation must be in similar units. When you say "actual" KW, take care that the value of COP is based on all the electrical input into the system, not only the compressor motor but also all the motors that are within the system such as, but not always, the motors that run the pumps, water and refrigerant, and fans, evaporators and condensers, and electrical controls.

  3. #3
    Join Date
    Mar 2006
    Location
    UK
    Age
    65
    Posts
    92
    Rep Power
    19

    Re: System capacity

    Thanks for that, have been playing around with a mollier chart and noticed that, just wanted it to be confirmed
    if you cant't fix it don't

Similar Threads

  1. Replies: 3
    Last Post: 29-04-2010, 10:30 AM
  2. how to calculate system capacity
    By pramodpatil in forum Fundamentals
    Replies: 3
    Last Post: 17-06-2009, 10:38 AM
  3. Replies: 3
    Last Post: 28-01-2009, 06:34 AM
  4. Replies: 14
    Last Post: 01-06-2007, 04:53 AM
  5. capacity control for 100% fresh air dx system
    By coztemur in forum Air Conditioning
    Replies: 5
    Last Post: 26-03-2007, 07:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •