17-02-2011, 06:30 AM #1
System capacity
Hi can any one help
If you divide the net refrigeration effect by the COP do you get the actual Kw of the system, if not is there a formula to find it, many thanks
if you cant't fix it don't
-
17-02-2011, 09:33 PM #2
Re: System capacity
You are correct. By definition COP = Energy output divided by energy input. Thus energy input is equal to refrigeration energy putput divided by COP. Of course, all the terms in the equation must be in similar units. When you say "actual" KW, take care that the value of COP is based on all the electrical input into the system, not only the compressor motor but also all the motors that are within the system such as, but not always, the motors that run the pumps, water and refrigerant, and fans, evaporators and condensers, and electrical controls.
-
18-02-2011, 07:00 AM #3
Re: System capacity
Thanks for that, have been playing around with a mollier chart and noticed that, just wanted it to be confirmed
if you cant't fix it don't
Similar Threads
-
Heat pump-cooling and heating capacity and capacity of compressor
By sale in forum FundamentalsReplies: 3Last Post: 29-04-2010, 10:30 AM -
how to calculate system capacity
By pramodpatil in forum FundamentalsReplies: 3Last Post: 17-06-2009, 10:38 AM -
What if we put higher capacity compressor in system designed for low capacity compres
By ractaan in forum FundamentalsReplies: 3Last Post: 28-01-2009, 06:34 AM -
change R22 DX system to R22 4:1 pump recirculation system
By JERRYCOOL in forum IndustrialReplies: 14Last Post: 01-06-2007, 04:53 AM -
capacity control for 100% fresh air dx system
By coztemur in forum Air ConditioningReplies: 5Last Post: 26-03-2007, 07:52 PM