    evacuation question
    for residential a/c systems is it better to evacuate once for a long period of time or triple evacuate for short periods?
    Oct 2006
    1,847
    Re: evacuation question
    I think different people will give you different answer.
    I have always been told that if possible, tripple vac. It is more effective than a
    deep vac, but the last vac must always be below 2 Torr (lower is even better).
    The reason behind this is the OFN that you break the vac with. Because it is dry
    it absorbs moisture and carries it out and each vac removes a little more moisture than
    the last.
    But if time is not a factor then put it on vac for 24 hours and suck the thing inside out .
    Somtimes you have no option.
    All the best
    taz
    Oct 2008
    mallorca, spain,
    75
    770
    hi taz, as allways you are spot on, I had tripple vaced for 40 years , but with the advent of better vac pumps , it is said that one vac is now sufficiant< if lower enough< hope you have enough work to keep you out of troble< sedgy,
    Sep 2003
    ISRAEL
    72
    4,266
    The only thing I can add here is my advice, get a good and big 100mm vacuum gauge.
    It will show you if you have moisture in the system and how deep is your vacuum.
    Just remember - Never charge the system while vacuum gauge is connected.
    May 2008
    Midlands
    27
    I have never seen any evidence for triple evacuation? I am not convinced that OFN carries out moisture when it is released.
    I say go for a long deep vac every time.
    Apr 2008
    Southampton, England
    49
    1,045
    35
    This has puzzled me because of the conflicting theories.
    At college I was told that OFN was introduced from high to low side to push all the bad stuff to the larger pipe making it easier for the vac pump to get it out and OFN had no absorption properties.
    Have always kept an open mind on this. In practice I bear in mind what the wife says to me - go long, go deep.
    Cheers,
    Andy.
    3,362
    generally only due vac test to dry systems , a triple evac as well. As for leaks, not a good test. effectively a negitive 15 psig pressure test. Unless you want to scan vac gauge for a month you will see naf all changes. HP testing above operating conditions is the only real check
    Split Croatia
    6,175