    evacuation question



    for residential a/c systems is it better to evacuate once for a long period of time or triple evacuate for short periods?



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: evacuation question

    .

    I think different people will give you different answer.

    I have always been told that if possible, tripple vac. It is more effective than a
    deep vac, but the last vac must always be below 2 Torr (lower is even better).

    The reason behind this is the OFN that you break the vac with. Because it is dry
    it absorbs moisture and carries it out and each vac removes a little more moisture than
    the last.

    But if time is not a factor then put it on vac for 24 hours and suck the thing inside out .

    Somtimes you have no option.

    All the best

    taz

    .
    Last edited by taz24; 17-03-2011 at 03:50 PM.

  3. #3
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: evacuation question

    hi taz, as allways you are spot on, I had tripple vaced for 40 years , but with the advent of better vac pumps , it is said that one vac is now sufficiant< if lower enough< hope you have enough work to keep you out of troble< sedgy,

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: evacuation question

    The only thing I can add here is my advice, get a good and big 100mm vacuum gauge.
    It will show you if you have moisture in the system and how deep is your vacuum.
    Just remember - Never charge the system while vacuum gauge is connected.

  5. #5
    Join Date
    May 2008
    Location
    Midlands
    Age
    57
    Posts
    27
    Rep Power
    0

    Re: evacuation question

    I have never seen any evidence for triple evacuation? I am not convinced that OFN carries out moisture when it is released.
    I say go for a long deep vac every time.

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,044
    Rep Power
    35

    Re: evacuation question

    This has puzzled me because of the conflicting theories.

    At college I was told that OFN was introduced from high to low side to push all the bad stuff to the larger pipe making it easier for the vac pump to get it out and OFN had no absorption properties.
    Have always kept an open mind on this. In practice I bear in mind what the wife says to me - go long, go deep.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: evacuation question

    generally only due vac test to dry systems , a triple evac as well. As for leaks, not a good test. effectively a negitive 15 psig pressure test. Unless you want to scan vac gauge for a month you will see naf all changes. HP testing above operating conditions is the only real check