    Dear friends,



    As you know Bitzer compressors has two motors for each compressor.
    By eg. 6H-35.2Y motor 35 HP AND 6h-25.2Y.

    The ranges is similary between evaporating -10 and -40 C and condensing 35-50 C temperature R 404A.

    My question is:

    Could I use the smaller motor (25 HP)? The application is an room ready to work also 0C and -18C of course using EXV Alco or Danfoss.

    Theroretically , in heavy working conditions for this compressor to/tk: -5/+50C, if accidentally gets, the pressure is big enough to burn out my motor.

    Even this I’ve seen other big companies like LINDE, especially, uses only small motors for Bitzer compressors?

    Is there any trick?

    Your experience could help me.



  2. #2
    Join Date
    Mar 2009
    Location
    Chicago, Il
    Age
    60
    Posts
    6
    Rep Power
    0

    Re: using small Bitzer( Motor2) for MT application

    1) The dividing line between LT & MT, or in your case Motor 1 & 2 (on avg.) is a ~(-5C) +23f - the caveat is that it depends on your SCT and Refrigerant.
    2) Download the Bitzer Software (for free) and run it....it CLEARLY spells it out for you.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: using small Bitzer( Motor2) for MT application

    The trick is using crankcase pressure regulators to limit the current draw during pull down and after defrost loads. Recommend checking the free software as mentioned in earlier post/ reply by Mr Freeze.
    Using MOP expansion valves can also reduce compressor loading.
    Last edited by Magoo; 16-02-2011 at 06:40 AM. Reason: addition

Similar Threads

  1. co2 compressor & application
    By ryanzhao in forum New Technologies
    Replies: 2
    Last Post: 20-09-2010, 06:29 PM
  2. Replies: 4
    Last Post: 26-07-2010, 09:08 AM
  3. Use of R22 compressor in R12 application?
    By flintsys in forum Commercial
    Replies: 45
    Last Post: 13-04-2010, 07:43 PM
  4. HBP compressor used in LBP application
    By Beltdrive in forum Fundamentals
    Replies: 12
    Last Post: 19-08-2008, 10:34 AM
  5. Job application
    By bojan in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 30-11-2005, 09:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •