    Could anybody tell me is there any recommendation for a refrigerant pressure drop in the condenser and evaporator? What are the common values? I dont need it for a particular project, just for an information and orientation
    BR to all


    Be careful about reading health books. You may die of a misprint.

  2. #2
    Join Date
    Dec 2008
    Location
    India, USA
    Age
    39
    Posts
    37
    Rep Power
    0

    Re: pressure drops

    It depends on the size of the condenser or evaporator.
    The smaller the pressure drop, is the better.
    Usually it lies in Pascals for smaller condensers/evaporators say around 50000 Pascals for 200 kg/hr.
    It will not be in bar or Mpa level. Anything above 0.5 bar is poor design for smaller condensers.

    The pressure drop is directly related to design of heat exchanger and mainly due to the losses due to friction and corners/flow path.

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: pressure drops

    Pressure drop between 2 points of the pipe depends on the flow rate in it.

  4. #4
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: pressure drops

    Hi Astoguro,
    Acceptable pressure drops in Condensers 5 to 15 PSI (refrigerant side)
    Acceptable pressure drops in evaporators 2.5 to 10 PSI (refrigerant side)

    Please note that the pressure drop across finned tube heat exchangers is directly related to the coil circuiting, the mass flow and the number of feeds.

    Best regards
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  5. #5
    Join Date
    Dec 2008
    Location
    India, USA
    Age
    39
    Posts
    37
    Rep Power
    0

    Re: pressure drops

    Thats little over 1 bar for Cond and 0.5 bar for Evap. I agree.
    Thanks for the info.

  6. #6
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: pressure drops

    You are welcome
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  7. #7
    Join Date
    Nov 2010
    Location
    Germany
    Age
    39
    Posts
    120
    Rep Power
    14

    Re: pressure drops

    Thanks guys...I wondered because i have done some calculations in Solkane for a refrigerant cycle because i needed a capacity of the condenser for one building to preselect the pumps and to see is it really worth of doing the Geothermal energy for cooling ad therefore i needed figures...Thanks
    Be careful about reading health books. You may die of a misprint.

Similar Threads

  1. Sump Pressure > Suction Pressure
    By schquenz in forum Air Conditioning
    Replies: 7
    Last Post: 04-08-2010, 01:37 PM
  2. high suction pressure and low head pressure
    By david ashley in forum Trouble Shooting
    Replies: 2
    Last Post: 05-08-2009, 06:26 PM
  3. Reasons for High Pressure / Low Pressure Trip outs
    By majikman in forum Air Conditioning
    Replies: 19
    Last Post: 02-02-2007, 08:47 PM
  4. Thanks god, the copper price drops a little
    By chistine in forum Air Conditioning
    Replies: 1
    Last Post: 17-11-2006, 08:18 AM
  5. pressure and temperature drops in R22 evaporator
    By fedri in forum Refrigerants
    Replies: 7
    Last Post: 09-07-2006, 03:44 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •