Thread: 23XL Carrier Chiller
12-02-2011, 01:20 AM #1
Hi Folks,
I'm new here and it's my first post. I'm from Brazil and need Help in a Carrier 23XL that i'm working on.
Actually machine is running but i have a alert message "High condenser pressure". I read some parameters that may help all:
Evaporator Refrig temp: 11,3c
Evaporator Pressure: 606,8 Kpa
Condenser Refrig Temp: 41,6c
Condenser Pressure: 1490,7Kpa
Discharge Temp: 56,8c
Oil Sump Temp: 56,8c
At Pic II i also have:
CHW in: 18,3c
CHW out: 15c
CDW in: 27c
CDW out: 34c
MTR AMP 80%
So if any one have ideas to help my chiller i would apprechiate a message.
Thanks in advanced!
12-02-2011, 11:46 AM #2
Re: 23XL Carrier Chiller
Your condenser water temperature is quite high, are these sort of temps normall in Brazil? here in the UK 17-20c is normall. What is your refrigerant type and cooling setpoint?
12-02-2011, 11:21 PM #3
Assuming its R22 and if the comp is not 100% loaded then you have a low condenser water flow problem with 7 C Delta T, software is probably not allowing the compresser to load up due to high condensing pressure.
13-02-2011, 04:24 PM #4
Condenser Refrig Temp: 41.6 c
CDW out: 34c
DT 7.6 ° C
DT THE MAYOR SHOULD BE A 5 ° C to my point of view you dirty condenser incrustation
13-02-2011, 07:20 PM #5
Actually february is summer in Brazil so external temperature is quite high around 34c.
Refrigerant is R-22.
To be honest my first guess was dirty condenser, but i am not sure.
14-02-2011, 06:30 PM #6
Yep, rod the condenser and check your flow rate
Carrier 23xl chiller-Low discharge superheat alarms
By Bradysmill in forum Trouble ShootingReplies: 7Last Post: 25-04-2010, 07:43 PM -
Carrier 23xl stuck float valve ???
By matt57 in forum Trouble ShootingReplies: 0Last Post: 27-03-2010, 11:14 PM -
Carrier 23xl/turbocor retrofit
By milar in forum New TechnologiesReplies: 1Last Post: 28-09-2009, 08:44 AM -
how to remove carrier compressor from 23xl
By hvacdoctor in forum Trouble ShootingReplies: 11Last Post: 15-02-2009, 07:43 PM
