    23XL Carrier Chiller



    Hi Folks,

    I'm new here and it's my first post. I'm from Brazil and need Help in a Carrier 23XL that i'm working on.

    Actually machine is running but i have a alert message "High condenser pressure". I read some parameters that may help all:

    Evaporator Refrig temp: 11,3c
    Evaporator Pressure: 606,8 Kpa
    Condenser Refrig Temp: 41,6c
    Condenser Pressure: 1490,7Kpa
    Discharge Temp: 56,8c
    Oil Sump Temp: 56,8c

    At Pic II i also have:

    CHW in: 18,3c
    CHW out: 15c
    CDW in: 27c
    CDW out: 34c
    MTR AMP 80%

    So if any one have ideas to help my chiller i would apprechiate a message.

    Thanks in advanced!



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: 23XL Carrier Chiller

    Your condenser water temperature is quite high, are these sort of temps normall in Brazil? here in the UK 17-20c is normall. What is your refrigerant type and cooling setpoint?
    Last edited by james10; 13-02-2011 at 03:23 PM.

  3. #3
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: 23XL Carrier Chiller

    Assuming its R22 and if the comp is not 100% loaded then you have a low condenser water flow problem with 7 C Delta T, software is probably not allowing the compresser to load up due to high condensing pressure.

  4. #4
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: 23XL Carrier Chiller

    Condenser Refrig Temp: 41.6 c
    CDW out: 34c
    DT 7.6 ° C
    DT THE MAYOR SHOULD BE A 5 ° C to my point of view you dirty condenser incrustation

  5. #5
    Join Date
    Jul 2010
    Location
    Brasil
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: 23XL Carrier Chiller

    Actually february is summer in Brazil so external temperature is quite high around 34c.
    Refrigerant is R-22.
    To be honest my first guess was dirty condenser, but i am not sure.

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: 23XL Carrier Chiller

    Yep, rod the condenser and check your flow rate

Similar Threads

  1. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  2. Carrier 23xl stuck float valve ???
    By matt57 in forum Trouble Shooting
    Replies: 0
    Last Post: 27-03-2010, 11:14 PM
  3. Carrier 23xl/turbocor retrofit
    By milar in forum New Technologies
    Replies: 1
    Last Post: 28-09-2009, 08:44 AM
  4. how to remove carrier compressor from 23xl
    By hvacdoctor in forum Trouble Shooting
    Replies: 11
    Last Post: 15-02-2009, 07:43 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •